Ground (Earthing) to Neutral Voltage

08/10/2010 3:03 AM

Hi, everybody

I have two ups, both are connected to a power socket(15amps) having neutral to earthing voltage is shown by meter is 6V. When are we measuring the neutral to earthing voltage in one ups(6kva,dc input 110v) output it is showing 6V,but in another ups(5kva,dc input 48v) output ,it is showing 0.002V.why both are showing different values. May any one help me?

Thanking you.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#1

Re: ground(earthing) to neutral voltage

08/10/2010 3:32 AM

Are both UPS are properly earthed to the same earth or separated earth.?

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply
Associate

Join Date: Aug 2010
Location: bhubaneswar
Posts: 34
Good Answers: 1
#2
In reply to #1

Re: ground(earthing) to neutral voltage

08/10/2010 4:37 AM

yes, both ups are connected to the same earthing point properly.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: ground(earthing) to neutral voltage

08/10/2010 5:05 AM

If both are properly earthed, then why is this number of any interest?

The purpose of the earth conductor is to operate the circuit protective device(s) in the event of a fault.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Popular Science - Evolution - New Member Popular Science - Weaponology - New Member

Join Date: May 2006
Location: The 'Space Coast', USA
Posts: 11119
Good Answers: 918
#4

Re: ground(earthing) to neutral voltage

08/10/2010 6:20 AM

Do you get the same 6 VAC at the wall socket with the UPS unplugged?

Register to Reply
Associate

Join Date: Aug 2010
Location: bhubaneswar
Posts: 34
Good Answers: 1
#5
In reply to #4

Re: ground(earthing) to neutral voltage

08/10/2010 6:29 AM

yes sir,I am getting 6vac at the wall socket with the both ups unplugged.

Register to Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#6
In reply to #5

Re: ground(earthing) to neutral voltage

08/10/2010 6:46 AM

dear,

earth connectivity of 6V socket is not proper. Since, 2nd socket has 0.002 V with the same electrode.

Just check - earth conductor continuity from 6V socket up to the electrode, ( wire must run seperately - direct from socket to earth & nott via other circuits )

If confident about the earth wire cotinuity, then just replace the socket. Earth PIN may not be proper.

I am sure, your problem will be solved.

__________________
Exploring the Science of Electricity
Register to Reply
3
Guru
Popular Science - Evolution - New Member Popular Science - Weaponology - New Member

Join Date: May 2006
Location: The 'Space Coast', USA
Posts: 11119
Good Answers: 918
#7
In reply to #5

Re: ground(earthing) to neutral voltage

08/10/2010 8:32 AM

Like Harry said, the problem most likely is in one or more receptacles or the main breaker box.

The following recommendations are for academic discussion only. It is highly advisable to employ a competent and licensed electrician to diagnose and repair faulty wiring. Electricity can kill!

In the US and most countries there is a hot or power wire (black) and a neutral wire (white). As a safety, an uninsulated ground wire is also run with the hot and neutral wires. Ideally, the ground and neutral wires should be at the same electrical potential (0 volts).

At the main breaker box the neutral wires and the ground wires from all branching circuits are tied to one large buss bar.

Typically, outlet boxes are daisy chained from a particular breaker circuit. Each breaker controls multiple outlets or switches. I would first identify the breaker that controls the known bad outlet and subsequently identify each outlet on that chain, which will be easy to do once you flip off the controlling breaker.

Tag each outlet affected by the breaker and tag the breaker that controls it. This makes it easy for the electrician to do his job. Note, overhead light sockets and wall switches may also be on the same circuit.

The ground problem probably lies with one outlet and subsequent outlets down the chain will exhibit the same problem. The outlet that is closest to the breaker that has the issue probably has a loose ground wire. Typically, the ground from the feeding circuit is twisted together with the ground wire feeding the next circuit in the chain. Sometimes the two are tied together at the outlet ground screw. Chances are oxidation of the copper or a loose ground screw or twisting of the wire has introduced resistance in the connection. It is also possible that daisy chained neutral wires may be at fault.

If all outlet connections are good, the source of the problem may be at the breaker box where the neutral and ground are connected.

Again, I am not advocating that you play electrician and try to resolve the problem yourself. A trained electrician is a better resource to fix the problem and he also assumes all liability for the work he does should something go very bad during or after the repair.

Should you attempt to repair it and, for example, a subsequent fire takes place, you can legally be held liable for any damage, injury, or deaths that result. Welcome to the world of litigation. Additionally, you can also electrocute and/or severely kill yourself!

Register to Reply Good Answer (Score 3)
Associate

Join Date: Aug 2010
Location: bhubaneswar
Posts: 34
Good Answers: 1
#8
In reply to #7

Re: ground(earthing) to neutral voltage

08/10/2010 9:15 AM

sir ,my doubt is here .....

why does difference of neutral to earthing voltage in both ups output? while both ups are connected to same parallel socket one is showing 6vac and another is showing 0.002vac.I have interchanged the power connector is showing same problems.(But main power socket (where is the ups plugged ) has 6vac in neutral to earthing.)

Register to Reply
Guru
Popular Science - Evolution - New Member Popular Science - Weaponology - New Member

Join Date: May 2006
Location: The 'Space Coast', USA
Posts: 11119
Good Answers: 918
#9
In reply to #8

Re: ground(earthing) to neutral voltage

08/10/2010 10:40 AM

First, did I understand you correctly when you said the 6 VAC is present at the wall outlet or did you mean that the 6 VAC is present at the UPS, regardless if the UPS is plugged in or not?

My guess is, since you stated that the 6 VAC potential between ground and neutral is present at the wall outlet with both UPSs disconnected, the two UPS are internally wired slightly different or an internal component may be bad in the one.

Another tact to try to isolate the problem:

Try the two UPSs on a completely different circuit (different breaker or even another house).

If they both work correctly, then you can be sure it is the house wiring.

Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Dec 2009
Location: San Antonio, TX USA
Posts: 844
Good Answers: 29
#10
In reply to #9

Re: ground(earthing) to neutral voltage

08/10/2010 11:19 AM

Did anyone say in all of that if he lived in an apartment complex or condo. Might have a bearing on the discussion.

__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Register to Reply
Guru
Popular Science - Evolution - New Member Popular Science - Weaponology - New Member

Join Date: May 2006
Location: The 'Space Coast', USA
Posts: 11119
Good Answers: 918
#11
In reply to #10

Re: ground(earthing) to neutral voltage

08/10/2010 3:23 PM

If that was true I would be giving some people too much credit. ;-)

Register to Reply
Commentator

Join Date: Mar 2007
Location: Tex us
Posts: 57
Good Answers: 1
#12
In reply to #11

Re: ground(earthing) to neutral voltage

08/11/2010 3:39 AM

Dear AH.. hat's off to you. Your knowledge base exceeds my expectations of your age in the photo! MIT grad? I'm the one who "learnt" OHM's law the hard way back when they had awesome flyback voltages to play with and purdy blue lights inside those vacuum tube rectifiers. (X-rays?) Yes, I was the teenaged mad experimenter who snap, crackled & popped every immaginable device of the era. I wonder when that 60 hz humm's gonna stop?

Seriously though, what are your thoughts on negating entropy?

I know, they say it can not be done. Who's they?

__________________
me thinks, therefore I am - I think?
Register to Reply
Guru
Popular Science - Evolution - New Member Popular Science - Weaponology - New Member

Join Date: May 2006
Location: The 'Space Coast', USA
Posts: 11119
Good Answers: 918
#15
In reply to #12

Re: ground(earthing) to neutral voltage

08/11/2010 8:10 AM

"Seriously though, what are your thoughts on negating entropy?"

A good breakfast!

You can't effectively take on the day if you are not properly nourished!

------

When I was in high school I met this guy that introduced me to building tube amps. That was how my electronics education actually started. To me they were really cool and exotic. ICs and transistors were too passé. I just completed a 60 WPC stereo tube amp from scratch (well, I did not wind the transformers) last Fall using the old KT88s just to recapture the magic again. Fun project and I learned a lot.

It sounds like you had a great childhood and I can see engineering was already running through your blood at an early age. ;-)

My understanding is the blue inside the tubes is a combination of trace gasses and other contaminants that are attached to the metal and glass of the tube. No audio, radio, or TV tube that I know of gets enough voltage to generate X-rays.

Register to Reply
Associate

Join Date: Aug 2010
Location: bhubaneswar
Posts: 34
Good Answers: 1
#13
In reply to #9

Re: ground(earthing) to neutral voltage

08/11/2010 3:58 AM

First of all thanks to all and specially to you for best cooperation.

sir

I have checked in different place it is showing same problems whatever it was showing but instead of 6vac it showing 1.3vac equal at the main circuit breaker(neutral to earthing voltage) I think both ups are designed in different way.one ups has battery input 110v dc it means it may has auto transformer and another ups has battery input 48 v dc ,it means it it is using step down transformer .conclusion is that auto transformer has common neutral for primary and secondary winding while step down has seperate winding that why one ups(having auto transformer) is directly passing the neutral to earthing voltage and another ups (having step down transformer) is not passing to the output. Am I right?

Register to Reply
Guru
Popular Science - Evolution - New Member Popular Science - Weaponology - New Member

Join Date: May 2006
Location: The 'Space Coast', USA
Posts: 11119
Good Answers: 918
#16
In reply to #13

Re: ground(earthing) to neutral voltage

08/11/2010 8:17 AM

Vsar brings up a good point. Have you measured the output of the UPS under load?

If you unplug the UPS and measure its output, does it still have the difference between neutral and ground?

Maybe it is a good time to consider calling or writing the manufacture. Sometimes you can get a tech or an engineer that can help you.

Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1271
Good Answers: 27
#14

Re: Ground (Earthing) to Neutral Voltage

08/11/2010 8:02 AM

Your voltage measuring device may just be picking up / displaying stray voltage readings (not real) coming from oscillators (chopper circuits) built in to the UPS units??

__________________
vsar
Register to Reply
Power-User

Join Date: Jun 2010
Posts: 344
Good Answers: 17
#20
In reply to #14

Re: Ground (Earthing) to Neutral Voltage

08/27/2010 7:10 PM

Good point. Do NOT use a DVM to measure this voltage. Use a good old-fashioned analogue meter, because it is not sensitive to odd hi-impedance signals.

Register to Reply
Power-User
Hobbies - HAM Radio - New Member

Join Date: Oct 2008
Location: Houston, Texas
Posts: 252
Good Answers: 5
#17

Re: Ground (Earthing) to Neutral Voltage

08/11/2010 11:38 PM

The voltage you are seeing at the wall socket between neutral and ground is due to the voltage drop in the neutral conductor. It will vary with the current on the branch circuit.

Six volts is kind of high but not unbelievable.

The difference between the UPSs is due to internal wiring differences. The UPS with the low neutral offset voltage has the output common bonded to the protective ground internally.

The UPS with 6 Volts between common and ground just passes the protective earth (ground) through without bonding it to the UPS output common.

Check it out and see if I am not right.

Sometimes, it think people get too theoretical and over analyze these things.

TT3

__________________
If the software can detect, compensate, avoid, or correct an anomalous condition in the system, it is, by definition, a software problem-regardless of the root cause. In the long run, for most classes of problems, it is cheaper to fix it in the SW
Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#18

Re: Ground (Earthing) to Neutral Voltage

08/12/2010 5:58 AM

Dear Manvendra,

You may check the following points to overcome your problems :

1) In power socket, in opencircuit condition( i.e. on load is connected in the socket), if you find N- E voltage is 6volt A.C., the wiring connections are not healthy. You must check the earthing conneciton, looseness in Neutral connection, conditon of Earth Staton itself It is better to measure the Earth resistance value by a Earth resistance tester. By physical as well as electrical checking methods, you may find out the location of looseness in Neutral in neutral connetion.

2)In the UPS you may please check the mettalic screen between two windings is properly connected to transformer body and transformer body is properly earthed.

__________________
Manindra
Register to Reply
Participant

Join Date: Aug 2010
Posts: 1
#19

Re: Ground (Earthing) to Neutral Voltage

08/12/2010 10:46 AM

Dear Manvendra:

From the problem cited what I feel is that in first UPS (6kVA), there is no isolation between the input and output and the suplly side neutral and earth connections are coming through to the load side. In the second case (5kVA) total isolation is there between input & output by deriving seperate neutral at the transformer secondary.

Register to Reply
Anonymous Poster
#21

Re: Ground (Earthing) to Neutral Voltage

12/01/2010 3:27 AM

Dear sir

we are sarvice provider of chemical eartnig, plz call me on this number

Thanks and regards

pritam pradhan

9313183026

Register to Reply Off Topic (Score 6)
Register to Reply 21 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Hero (6); Anonymous Poster (1); BMB (1); harry potter (1); leskranes (1); manindra (1); manvendra (4); Phaddy (1); PWSlack (1); RDGRNR (1); Simon Wan (1); Turbotroll3 (1); vsar (1)