What kind of routine are you following for regular maintenance/inspection on your hermetically sealed transformers?
We are doing monthly routine inspections for leakages, and bushing cleaning and connection tightness.
Re: Transformer regular maintenance routine
08/11/2010 8:00 AM
dear,
this is a new concept, where there is not a regular periodic maintenance is required.
But, innovations & new ideas for reliability & life improvements, there is no end.
If the size of transformer is high , say more then 1 MVA, you may install the on line monitoring equipment of the transformer, that checks continuously
1. Oil gases - degradation of oil with time, which takes more then 5 years, if it is oil filled
2. Gas pressure, if it is SF6 Gas filled
3. Winding temperature rise
4. Earth leakages in winding
5. Insulation levels in Meg Ohms
Exploring the Science of Electricity
Good Answers: 181
08/11/2010 11:15 AM
If its hermetically sealed your doing more harm than good regular inspections degrade the seals. Again if hermetically sealed why do you need to clean the bushings ? ? ? There should be no ingress of contaminants
As to checking the tightness of the conections, are you using a touque wrench ? ? ? If not you will cause more damage due to stretching the conection bolts.
08/11/2010 11:44 PM
Our transformers are located outdoor where the atmosphere is highly polluted. So the bushings (which are exposed to the atmosphere) are observed monthly and also the transformer as a whole is inspected for any oil leakages.
Connection tightness is a routine inspection job where we are not really torquing the bolts. Connections are marked where the torquing was done the last time and it is inspected visually. You can check the tightness with hand or with any tool just to make sure nothing is really loose.
Good Answers: 117
08/12/2010 1:56 AM
Hi
You've covered it, you cannot do any more on your transformers than you are already doing.
Just be careful when checking the connections that you do not over tighten and/or put a strain on the connection, I think you mean you are cleaning the insulator bushes, which is a good thing, just use a clean cloth or brush... DO NOT use cleaning chemicals, they attract even more dirt, and continue to check for those leaks
08/12/2010 3:52 AM
Hai See above file. I will send by mail, If it is not viisible properly. Pls give ur mail ID.
09/04/2010 11:00 PM
Dear sir, can you kindly mail the maint schedule at my mail id ash2kom@yahoo.co.in I am staying in a society and feel that maint is not being carried out so this will help the management to work out a plan. Thanks chachu
05/01/2011 5:15 AM
Can you please send me too? <email removed> Thanks..
CR4 Admin - email address removed
From the CR4 Rules: Do not post phone numbers or email addresses. The CR4 Admin will delete all phone numbers posted in threads or comments, and we strongly urge you not to put up email addresses. You can share this information via the CR4 internal messaging system.
Register to Reply 7 comments
bethini.hanumanthu (1); brich (1); chachu (1); harry potter (1); kobavr (1); Suleman (1); TonyS (1)