Installation of 500kva dg

08/11/2010 10:17 AM

what is the capacity of copper cable that can be used for 500kva dg?

trivandrum,kerala,india

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: installation of 500kva dg

08/11/2010 10:26 AM

Typically, 3 Runs of 3.5c & 300 sq.mm YFY Cable

Register to Reply
Participant

Join Date: Aug 2010
Posts: 3
#3
In reply to #1

Re: installation of 500kva dg

08/11/2010 10:40 AM

size of copper that can be used instead of aluminium

Register to Reply
Anonymous Poster
#5
In reply to #3

Re: installation of 500kva dg

08/11/2010 10:57 AM

Yes! Copper@ If aluminium, it should be 3R x 3.5 core x 400 sq.mm cable.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: installation of 500kva dg

08/11/2010 10:35 AM

→ British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster
#4

Re: Installation of 500kva dg

08/11/2010 10:52 AM

wikipedia

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#6

Re: Installation of 500kva dg

08/11/2010 8:51 PM

Quote EE65 "Typically, 3 Runs of 3.5c & 300 sq.mm YFY Cable"

If that for a generator output of 208 v, 240 v, 415 v, 480 v or 600 volts or some other voltage?

Register to Reply
Anonymous Poster
#7
In reply to #6

Re: Installation of 500kva dg

08/11/2010 9:16 PM

OP is from India. In India, 500kVA DG sets come with 415V Output Voltage. So, the cable size given is for an output voltage of 415V, 50 Hz.

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#8

Re: Installation of 500kva dg

08/12/2010 2:07 PM

You should give the current rating shown.in the nameplate.Afterwards decide on type of cable(insulation,single or 4core,method of laying,amb temp,length etc) and by referring BS 7671 you can select.

__________________
pnaban
Register to Reply
Participant

Join Date: Aug 2010
Posts: 3
#9
In reply to #8

Re: Installation of 500kva dg

08/17/2010 3:12 AM

750A amps

Register to Reply