Siemens Master Drive

08/11/2010 4:00 PM

We experience some problems with a siemens 2000 Kw master drive:F025

We found a cable with the red phase down to earth. The cable was repaired but still the drive trips on F025

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Siemens Master Drive

08/11/2010 8:42 PM

Did you try calling Siemens?

F025 is usually a failed IGBT transistor. Your bad cable probably fried it, you will need to get the drive repaired by a qualified technician, and I would recommend replacing all of the transistors because a fault like that usually damages several, it's only one that fails first. So if you only replace one, you will be calling the technician out again later to replace the others one by one. Just bite the bullet and get it over with.