Running PF Calculation

08/11/2010 8:31 PM

i have a 200KVA gen, a pf of 0.8 to have a true rated power out put of 160W max. if i load the generator to get a true power output of 80W, will i be correct by saying that the load pf is 80/200 = 0.4 and how does this affect the supply and the load?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: runing pf calculation

08/11/2010 8:46 PM

Quote "I have a 200KVA gen, a pf of 0.8 to have a true rated power out put of 160W max. if i load the generator to get a true power output of 80W, will i be correct by saying that the load pf is 80/200 = 0.4 and how does this affect the supply and the load?"

Your generator is rated at 200 KVA if the PF = 0.80. If the PF of the load was 1.0 the generator would be capable of 200 KVA = 200 KW. KVA = KW/pf. Eg 80 kw at 0.80 PF would equal 80 kw/0.80 = 100 KVA. The load determines the Pf, not the generator.

Register to Reply Score 1 for Good Answer
Participant

Join Date: Aug 2010
Posts: 3
#2

Re: Running PF Caclculation

08/11/2010 11:57 PM

200kVA is the generator's capacity.

at 0.8 p.f:

kVA = kW x P.f
200 = 160 x 0.8

Whatever load there is on the generator, it should change the current value (whereas the system voltage remains the same). Power factor is usually set at a fixed value i.e. 0.8 or depending upon if there is requirement for reactive energy that has to be exported.

"Load determines the supply".

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#4
In reply to #2

Re: Running PF Caclculation

08/12/2010 1:28 AM

Please recheck your equations.

kW = kVA x pf. Not the other way.

Also, the load decides the pf. If i have a high-inductance load like an induction furnace with pf ≈ 0.3, how can the generator keep supplying at 0.8 ?

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member Popular Science - Genetics - New Member Technical Fields - Technical Writing - New Member Safety - ESD - New Member Engineering Fields - Power Engineering - New Member

Join Date: Jul 2010
Location: INDIA MUMBAI
Posts: 67
#3

Re: Running PF Calculation

08/12/2010 1:15 AM

Depending upon the load pf.

you can adjust the generator p.f accordingly and run on any p.f with in the generator capability curve limit

__________________
Correct Me If Iam Wrong, Suggestions/Recommendations needs to be verified before implementation
Register to Reply
Participant

Join Date: Aug 2010
Posts: 3
#5

Re: Running PF Calculation

08/13/2010 2:06 AM

having said that about my question, i would rephrase by asking if power factor is constant through the process of generating and loading. i knw voltage is constant. current varies (depending on the load) but how about the pf, is it constant irespective of the load?

Register to Reply
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member Popular Science - Genetics - New Member Technical Fields - Technical Writing - New Member Safety - ESD - New Member Engineering Fields - Power Engineering - New Member

Join Date: Jul 2010
Location: INDIA MUMBAI
Posts: 67
#6
In reply to #5

Re: Running PF Calculation

08/13/2010 5:58 AM

you can run the generator on the fixed power factor mode if you want.

but with this you cannot control the voltage level at the switchgear.

voltage level will change. it will decrease if load is more reactive and it will increase if load is less reactive.

__________________
Correct Me If Iam Wrong, Suggestions/Recommendations needs to be verified before implementation
Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Aug 2010
Posts: 111
Good Answers: 2
#7
In reply to #6

Re: Running PF Calculation

08/14/2010 2:27 AM

as mentioned in the discussion...the load affects the pf..your effective VA is still the same..but your VAR varies...try looking at the impeadance triangle..you will find the answer there.

________________________________________

take care of your seconds and the minute will take care of itself...-LRN

19ΕΣ57

__________________
take care of your seconds and the minute will take care of itself..
Register to Reply
Register to Reply 7 comments

"Almost" Good Answers: