Total Dissolved Gas in Oil

08/12/2010 12:35 AM

I have a data recording dissolved Total Gas in oil which is measured online (every 15 minutes), but I am confused analyze it, because the profile fluctuates with a fairly large range. I think it is strange because with the added time of the operation of a transformer, the gas content inside the transformer tank should be increased. Is there someone who can explain to me why it fluctuate?

Register to Reply
Pathfinder Tags: total dissolved gas in oil
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#1

Re: Total Dissolved Gas in Oil

08/12/2010 10:50 AM

If the transformer is a sealed tank, the total gas value should not change drastically. There will be some fluctuation with the temperature of the oil, and the temperature will vary based on the loading, ambient conditions (temperature, day/night, sun/overcast, etc.) and whether or not the forced cooling (fans/pumps) is running.

A vented tank will show more fluctuation, but it should still follow a well-defined pattern due to the solubility of gas in the oil. Higher oil temperatures should lead to lower total gas, and lower temperatures should correspond to higher total gas.

If the total gas is rising, you should do a full dissolved gas analysis and compare it to a previous test. A rise in combustible gases (acetylene, ethylene, ethane) indicates arcing in the oil, and damage to the transformer is likely.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply
Active Contributor

Join Date: Jul 2010
Posts: 10
#3
In reply to #1

Re: Total Dissolved Gas in Oil

08/17/2010 12:41 PM

thanks

Register to Reply Off Topic (Score 5)
Active Contributor

Join Date: Jul 2010
Posts: 10
#5
In reply to #1

Re: Total Dissolved Gas in Oil

08/24/2010 2:12 AM

Can you explain to me why the amount of gas in the oil decreased with increasing temperature in the transformer oil (Higher oil temperatures should lead to lower total gas)? and please give me a reference that explains this phenomenon.

Thanks

Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#2

Re: Total Dissolved Gas in Oil

08/12/2010 12:32 PM

If a transformer is healthy, total gas should stay fairly constant (not increasing) unless there are causes to make it go up (heating, insulation breakdown, faults, etc.). Even if it were fluctuation due to changes in loading, temperature, or similar, the "inertia" of the oil mass would damp out any sudden changes.

Have you considered that your severe fluctuation could be a problem between the sensor and the monitoring unit? I presume these are low-level signals, maybe 0-1mA or millivolts, so some sort of damage to the wiring or connectors can cause strange readings. Wouldn't be the first time.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Active Contributor

Join Date: Jul 2010
Posts: 10
#4
In reply to #2

Re: Total Dissolved Gas in Oil

08/17/2010 12:41 PM

thanks