Every time we changeover the power from one generator to another the problem is always the sync out generator draw current from the sync in generator. I dont know what to do to make the transferring smooth and no gaining of power from the incoming generator. Until now we are shutting off the out going generator to avoid the power gain from incoming.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator

Join Date: Jul 2010
Location: South Windsor, CT USA
Posts: 67
Good Answers: 2
#1

Re: Drawing High Current

08/16/2010 12:45 PM

Sounds like you are out of sync., is the synchronization automatic or manual, if you don't have any lights or sync. scope there is a way to do it with two analog meters but I am reluctant to advise that.

Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#2

Re: Drawing High Current

08/17/2010 4:50 AM

dear,

In this case, it seems you have not installed the load sharing instruments.

You need to install the automatic KW sharing instrument, that gradually decreases the KW load of out going DG , & after some minimum set value of say, 15% of full load, that de couples the breaker of out going DG.

__________________
Exploring the Science of Electricity
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: Drawing High Current

08/17/2010 10:55 AM

Quite natural. If the synchronisation/de-synchronisation is manual, due to the "not-so-fast" response of the operator, the synch. out generator's voltage & frequency will decrement only slowly. Then it will become "sort-of" a load (both active load & recative load) on the synch. in generator.

It is strongly suggested that you go for auto-synch. as well as auto load sharing scheme to avoid this problem.