08/17/2010 1:30 PM

Hi all. what is the current rating busbar to be used in 500 kva transformer?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Transformer busbar

08/17/2010 1:39 PM

It dependes on the voltage of the winding connected to the busbar.

Try a search engine and look for rating charts or tables for busbars.

Yahlasit

Reply
Anonymous Poster
#2

Re: Transformer busbar

08/17/2010 11:06 PM

if you have 415 volts then 800 amps

Reply
Active Contributor

Join Date: Jul 2010
Location: Malaysia
Posts: 17
#3
In reply to #2

Re: Transformer busbar

08/17/2010 11:31 PM

guest,

pls consider also transformer's vector group (delta or wye connected) since it will affect each phase current.

Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#6
In reply to #2

Re: Transformer busbar

08/18/2010 9:28 AM

dear ,

what about the fault level capacity rating ?

what about the temperature rise limits ?

Then, you may need 1000A bus bar as well, for the same duty.

__________________
Exploring the Science of Electricity
Reply
Anonymous Poster
#4

Re: Transformer busbar

08/18/2010 7:51 AM

you may like to use 1000 A busbar at 380 volt

Reply
Power-User

Join Date: Mar 2010
Posts: 105
#5

Re: Transformer busbar

08/18/2010 7:57 AM

Dear Guest,

The FLA of 500 Kva Transformer @ 415 volts is 695 Amps to be specific.

Please add 20 % for any instantaneous loads - 695 x 1.2 = 834 Amps. The Busbar

can be rated for 800 A ( as pointed by one of our readers) or 850 Amps. The Size

will depend on the meterial copper or Aluminium. and the stacking factor.

Manroop.Chennai.

Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Aug 2010
Posts: 111
Good Answers: 2
#7
In reply to #5

Re: Transformer busbar

08/22/2010 9:44 PM

dear,

this may help...old method in sizing bus bar will be using 1.55A/sq.mm curent density...but a 1.0 A/sq. mm would be best suited for the calculation...this is to cope up with load growth and derating factors...

__________________
take care of your seconds and the minute will take care of itself..
Reply
Reply to Forum Thread 7 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); dj46 (1); harry potter (1); manroop (1); rockraiden (1)

Previous in Forum: Relay Logic Elevator Controller Using VF Motor Drive   Next in Forum: why use CT in series & PT in parallel

Advertisement