With a load rated 460kW, 480v, 3ph., would using (3) 4/0 THHN wires per leg @ aprox. 80' distance, (in conduit) be sufficient w/ a max. 700 amp sorce output? I say yes, some say no. I may be missing a calculation factor. Not sure.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
460 kw/0.48 x 1.730 x 0.79 pf = 700 amps. From table 310.16 NEC
4/0 thhn ampacity = 230 amps x 3 ckts = 690 amps assuming 3 ckts in 3 separate conduits. 4/0 is not large enough. Is this a continuous load(over 3 hrs)?
If load is continuous you need to use 700 amps x 1.25 = 875 amps
Require 3 ckts of 350 thhn or 4 ckts of 4/0 thhn. Are you using NEC table 310.16
Yes I was using the same chart, but out of the Uglys Elec. References book (2008). I actually used the 90degC chart @ 260A. I am a tech that was ask my input on this and will not have the final decission. This is an AC Drive feeding a Dyno. The wires actually existed for a 500kW, but was never powered up so it was questionable. It is YTD if it will run continuous or even hit full capacity.