Ampacity

08/19/2010 11:01 AM

With a load rated 460kW, 480v, 3ph., would using (3) 4/0 THHN wires per leg @ aprox. 80' distance, (in conduit) be sufficient w/ a max. 700 amp sorce output? I say yes, some say no. I may be missing a calculation factor. Not sure.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Ampacity

08/19/2010 12:33 PM

→ British Standard 7671.

AAAAAAAAAAAAAAAAAAAAAAAAAAAAAAArgh!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
3
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: Ampacity

08/19/2010 1:14 PM

460 kw/0.48 x 1.730 x 0.79 pf = 700 amps. From table 310.16 NEC

4/0 thhn ampacity = 230 amps x 3 ckts = 690 amps assuming 3 ckts in 3 separate conduits. 4/0 is not large enough. Is this a continuous load(over 3 hrs)?

If load is continuous you need to use 700 amps x 1.25 = 875 amps

Require 3 ckts of 350 thhn or 4 ckts of 4/0 thhn. Are you using NEC table 310.16

Juzdatech please reply to this post.

Table NEC 310.16

http://www.houwire.com/products/technical/article310_16.html

Register to Reply Good Answer (Score 3)
Member

Join Date: Aug 2010
Posts: 9
#3
In reply to #2

Re: Ampacity

08/19/2010 1:50 PM

Thanks wareagle,

Yes I was using the same chart, but out of the Uglys Elec. References book (2008). I actually used the 90degC chart @ 260A. I am a tech that was ask my input on this and will not have the final decission. This is an AC Drive feeding a Dyno. The wires actually existed for a 500kW, but was never powered up so it was questionable. It is YTD if it will run continuous or even hit full capacity.

Your reply was helpful.

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#4

Re: Ampacity

08/19/2010 2:52 PM

You can not use the 90C rating when making this calculation. It is only used when derating the conductor for temp and number of conductors in conduit.

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#5

Re: Ampacity

08/25/2010 2:41 PM

Will someone post the document titled"nec conductor sizing.htm" for the benifit all readers?.

__________________
pnaban
Register to Reply
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

juzdatech (1); pnaban (1); PWSlack (1); wareagle (2)