External Floating Roof Tanks

08/22/2010 4:39 AM

Recently we commissioned two 660 mbbl Double Deck External Floating Roof Tanks (88.5 mts x 22Mts) for Condensate storage and export. What's bothering us is that the center part of the deck the product is puking from the sleeves of the roof legs. the sleeve projection on the underside of the roof is 350mm, The local ambient temp normally peaks upto 40º C / 104º F, again Double deck should not have this as a contributing factor. The Condensate Sp. Gr. os 0.77. Can anyone faced similar situation?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Mechanical Engineering -

Join Date: Sep 2009
Posts: 1651
Good Answers: 71
#1

Re: External Floating Roof Tanks

08/22/2010 8:52 AM

If it is coming from the center only, check to see if your ladder isn't too heavy on the center and weighing it down too low. Should be easy to check with a lazer level moved around the outside and different parts measured in the center, or where the puking is occurring.

On a span that long, you could have buckling or warpage from the temperature, uneven weight distribution etc. I think the first step is to find out if it is lower than it should be anywhere.

Drew

__________________
Question: What is going on with the American's Government? Response: Who is John Galt?
Register to Reply Score 1 for Good Answer
Associate

Join Date: Jul 2010
Posts: 50
#2
In reply to #1

Re: External Floating Roof Tanks

08/23/2010 1:45 AM

Drew,

Thanks, unfortunately the ladder re-location is not an option. was trying to think of other ideas..maybe introduce some kind of sealing?

Register to Reply
Guru
Engineering Fields - Mechanical Engineering -

Join Date: Sep 2009
Posts: 1651
Good Answers: 71
#4
In reply to #2

Re: External Floating Roof Tanks

08/23/2010 2:18 AM

Like Abel said, make the legs longer. But first investigate to determine if that is your problem; the laser level trick should work, they have cool ones that emit a flat plane of light and all you have to do is walk around with a measuring stick and spirit level.

If the center does indeed depress a bit making the risers on the legs should solve the problem. Trying to seal it up is just a bandaid on the real problem and bandaids often fail.

If your problem is something different, you will need a different solution. After thinking for awhile I thought your problem could be from vapors or air accumulating under the center and forcing some product up the leg stacks. This could be solved by installing a vent for the floating pan's open center area (if your's is open underneath in the center). If you install a pressure/vacuum vent your evaporation will be minimal.

Drew

__________________
Question: What is going on with the American's Government? Response: Who is John Galt?
Register to Reply
Guru
Engineering Fields - Piping Design Engineering - New Member Egypt - Member - Member since 02/18/2007

Join Date: Feb 2007
Location: Cairo, Egypt
Posts: 1733
Good Answers: 248
#3

Re: External Floating Roof Tanks

08/23/2010 2:03 AM

The problem may be due to the excess weight of ladder affecting on the middle of floating roof as mentioned at post #1 of our friend Drew K. And this weight should be used and added to the weight of all components of floating roof, and this was necessary at the 1`st step of design

Another reason is the widely range of tank diameter 88.5 m (and in turn higher range of internal pontoon diameter, D2), where there must be an enough width of pontoon width W, during the 1st step of buoyancy calculation of floating roof..

This problem may be avoided if you stored a liquid with higher specific gravity than 0.77.

Using a sealing will not solve the problem, but I recommend enlargement of the height of legs' sleeves especially for those located at the middle of the floating roof, taking into consideration the gas free before welding

.........................................

__________________
It is better to be defeated on principles, than to win on lies!
Register to Reply
Associate

Join Date: Jul 2010
Posts: 50
#5
In reply to #3

Re: External Floating Roof Tanks

08/23/2010 5:03 AM

Excellent, Thanks Abdel and Drew, Looks like due to the fact that the roof are designed for submerged 75% (designer to confirm), maybe increasing the length of the sleeve would help. We are waiting for the tank designer to comeback with their opinions. Will post all about the outcome.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering -

Join Date: Sep 2009
Posts: 1651
Good Answers: 71
#6
In reply to #5

Re: External Floating Roof Tanks

08/23/2010 9:08 AM

Sounds good, I look forward to hearing what you use for a solution.

If your roof is 75% submerged you want to make sure your water drain is adequate and does not get plugged. I had to walk out on a roof that had about 16 inches of water on it across most of it's surface. It was designed with an outer ring of pontoons and an open center that accumulated water during a heavy storm when the drain was plugged with paint chips (from a previous repainting) dirt and bird excrement. We don't know how close it came to sinking but I was kinda scared walking out on it.

Drew

__________________
Question: What is going on with the American's Government? Response: Who is John Galt?
Register to Reply
Anonymous Poster
#7

Re: External Floating Roof Tanks

08/23/2010 3:22 PM

If it was the length of the roof sleeves, you should be seeing it in more areas than that shown in the pictures. Is it just in this one area or is it throughout the tank? If it is in this one area I have a few questions.

What size is your fill nozzle?

Does the fill nozzle have a diffuser on it?

Is the fill nozzle outlet in this location?

Does it only happen when filling the tank?

It could be that the fill nozzle is creating an agitation in the tank and this is forcing the product up the sleeves. This often happens with large fill nozzles not equiped with a diffuser.

Register to Reply
Associate

Join Date: Jul 2010
Posts: 50
#8
In reply to #7

Re: External Floating Roof Tanks

08/24/2010 7:57 AM

Filling nozzles has an extention of 4 to 5 mts into the tank internal which acts as a diffuser, morover the flow rate is very low (750 m³/Hr.) the nozzle size being 28" Ø the issue of turbulance etc does not arise. Outlet location is 90° to the inlet.

Looks like this is happening during both filling / emptying. Practically we cannot watch 100% by placing crews on top of the tank.

only at the centre portion of the deck the problem exists, the remaining part of the roof is OK with no issues, (saw that same issue during the first fill and did not repeat).

Register to Reply
Associate

Join Date: Jul 2010
Posts: 50
#9

Re: External Floating Roof Tanks

09/15/2010 4:24 AM

Guys, Came back from a short vacation, Visited the tank recently, what I saw was really good to share with all.

I would say that the puking was not the case, Due to extreme temperature and the product Sp. Gravity being 0.745 the product was actually evapourating. Local temperature around here touches 45ºC +, the vapours created at the shell contact points are making their way (path of least resistance) i.e to the central portion and exhaling thru those legs sleeves. Due to the presense of vapour socks and contineous flow of vapours were condensing and flowing as droplets from inside of these neoprene rubber socks.

What was decided was that we would wait for the coming months and observe the behaviour when the temp. falls below 30ºC. If this continuies the tank may require external insulation.

Please advice me if any one of you have some thoughts on this.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering -

Join Date: Sep 2009
Posts: 1651
Good Answers: 71
#10
In reply to #9

Re: External Floating Roof Tanks

09/15/2010 10:15 AM

Sounds good, much better than some of the thoughts we had.

You could try to seal up the leg sleeves better, if the evaporation is happening right at the legs. I thought the point to the floating roof was to reduce evaporation by reduction of the surface area exposed to evaporation. If the roof is not in contact with the product across it's surface you will get excess evaporation and it will come out anywhere it can escape.

45 C sucks. I endured that in Turkey, it gets into the mid 30's sometimes 40 here in Texas. I liked it best in England where it stayed in the 20's most of the time.

Drew

__________________
Question: What is going on with the American's Government? Response: Who is John Galt?
Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Abdel Halim Galala (1); Anonymous Poster (1); Drew K (4); JCS (4)

Previous in Forum: Tell Tale Hole Location   Next in Forum: Allowable Stress: High Pressure Pipe Design
You might be interested in: Storage Tanks and Process Tanks, Roof Curbs

Advertisement