hello,
Does anybody know where I can find a mathematical or graphical relation between current and torque (i.e. current-torque characteristics) for ac motors.
thanx
Re: How to calculate a current for a given torque
03/05/2007 9:37 AM
v You could get them from products specification or relative reference handbook. different type of ac motor has different cm curve. you can also use this formula M=aCI(fei)*cos(thita)
03/07/2007 3:08 AM
can you illustrate the formula for me:
what are the abbreviations for the consequent letters;M,a,C
thanx
Re: How to Calculate a Current for a Given Torque
03/06/2007 7:17 AM
From the manufacturers.
Torque and current are linearly related.
03/06/2007 8:03 AM
I do not know where you can find such an equation or graph. There are several factors to consider. Current will be different for different voltages. For instance, if you have a 5 hp 3 phase motor running on 460 volts, full load current will be about 6.5 amps. The same motor connected for 230 volts would draw about 13 amps. In addition to this, different types and efficiencys will develop their full load torque at different speeds (slip). Beyond that, there is a magnetization current that the motor needs before it can begin to produce any torque for the load. These factors vary with motor size and design.
03/06/2007 7:20 PM
The short answer is:
Rated torque of a motor = kW x 9550/rpm (at rated full speed)
rpm = 120 x f / P
kW is the motor kilowatts. 1kW = 1.3405 x Hp
where:
Hp is horsepower
f is electrical frequency (usually 60Hz in North America)
P is number of motor poles
Torque at any speed:
Not a simple answer - will depend on many variables. The following equation generally holds true for induction motors:
Torque = (1.5 x P x wm x Rr' x V1^2) / (w x slip x ((Rs + (Rr' / slip))^2 + XL^2)
(^2 means "squared")
where:
Torque: Motor torque at motor shaft, varying with slip. Unit: Nm
P: Number of poles of the motor
Rr': Total equivalent resistance of the rotor. Unit: ohms
V1: Applied line voltage at the stator terminals. Unit: Volts
w: Electrical frequency of applied current at the stator terminals. Unit: rad/s
slip: Motor slip
Rs: Internal total stator resistance. Unit: ohms
XL: Total equivalent leakage reactance referred to the stator. Uni: ohms
The long equation will give you the complex motor curve unique to each motor. I did a thesis on how to change the motor characteristic to accomplish various load-speed dynamic controls.
03/11/2007 3:13 PM
NICE!!!!!!!!!!!!!!!
ELECTRICAL AND MECHANICAL MEET AT LAST lol thanks
03/07/2007 8:13 AM
Our guest is correct. You can easily calculate the rated torque of a given motor. I misunderstood your question. I thought you wanted to calculate what the current would be for a motor when the load required less than the rated torque.
03/08/2007 8:27 AM
Mech.Power(KW)= Torque (Nm)xSpeed(RPM)/9550
Elec.Power= Mech.Power/Efficiency
Current=Elec. Power/Voltage for DC Motors
Current=Elec. Power/Voltage/Power Factor/1.7328
09/10/2007 1:14 PM
Just curious...
I was doing a motor calc... (been a long time) searched here and found this thread.
Where does the 1.7328 factor come from when calculating current?
Live Slow - Sail Fast
Good Answers: 804
09/10/2007 8:46 PM
It only applies when calculating for 3 phase systems. That is the square root of 3.