Anonymous Poster

CT Ratio

08/27/2010 11:49 AM

What is Principal of CT Ratio selection of Metering Cubical

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: CT Ratio

08/28/2010 9:27 AM

The primary current of the CT should be equal to the load current of the feeder or the nearest standard rating available and the secondary current of the CT should be that of the meter in the metering cubicle (1A or 5A).

Reply
Participant

Join Date: Aug 2010
Posts: 4
#2

Re: CT Ratio

08/31/2010 2:36 PM

"In general, ct ratios are selected to match the maximum load current requirements, i.e., the maximum design load current should not exceed the ct rated primary current. The highest ct ratio permissible should usually be used to minimize wiring burden and to obtain the highest ct capability and performance. The ct ratio should be large enough so that the ct secondary current does not exceed 20 times rated current under the maximum symmetrical primary fault current."