Selection of Neutral Size for Different Load Applications

08/27/2010 9:08 PM

Selection of Neutral Size for different Load Applications!

Earlier Neutral use to be half of the phase in busbars as well as Breakers
Now applications like IT/Data centers neutral rating is twice of Phases due to harmonice
Just want to know more details from the experts,
what else could be the factors affecting neutral selection!?

__________________
Please save the power for Next Generation- Do ur bit
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: Selection of Neutral Size for Different Load Applications

08/28/2010 8:48 AM
__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Selection of Neutral Size for Different Load Applications

08/28/2010 9:07 AM

Not to ignore the level of unbalance in the single phase load distribution and utilisation amongst the three phases.

Register to Reply
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member Popular Science - Genetics - New Member Technical Fields - Technical Writing - New Member Safety - ESD - New Member Engineering Fields - Power Engineering - New Member

Join Date: Jul 2010
Location: INDIA MUMBAI
Posts: 67
#3
In reply to #2

Re: Selection of Neutral Size for Different Load Applications

08/30/2010 1:10 AM

mostly as you said third harmonic is the major cause of heating of the neutral.......and then the unbalance single phase loading.

__________________
Correct Me If Iam Wrong, Suggestions/Recommendations needs to be verified before implementation
Register to Reply
Power-User

Join Date: Nov 2009
Posts: 198
Good Answers: 18
#4

Re: Selection of Neutral Size for Different Load Applications

08/30/2010 6:55 AM

Earlier half size neutrals were there because the installing electrician cut costs. Consider what would happen to the half size neutral if you had a fault on the "full size" conductor and the half size had to carry that fault current?

The neutral cable should be at least the size of the conductors. However, if you do have a system saturated with harmonic currents, you should calculate the neutral size (Some installers double the size of the neutral as a rule of thumb).