why 3rd harmonic current always flow in neutral of a star connected windings? why not in other 3 windings if transformer having isolated neutral????
Good Answers: 244
Re: Harmonic Current
09/22/2009 5:01 PM
Here is the explanation:
For Fundamental components:
In a three-phase, four-wire system, single-phase line-to-neutral load currents flow in each phase conductor and return in the common neutral conductor. The three phase currents are separated by 120°; and for balanced three-phase loads, they are equal. When they return in the neutral, they cancel each other out, adding up to zero at all points. Therefore, for balanced three-phase loads, neutral current is zero.
Mathematically,
Ia = I sin (wt)
Ib = I sin (wt - 120)
Ic = I sin (wt + 120)
In = Ia + Ib + Ic = I{ sin (wt) + sin (wt – 120) + sin (wt + 120)} = 0
For 2nd and all even Harmonic components:
For 2nd harmonic currents separated by 120°, cancellation in the neutral would also be complete with zero neutral current.
Mathematically,
Ia = I2 sin 2(wt) = I2 sin (2wt)
Ib = I2 sin 2(wt - 240) = I2 sin (2wt + 120)
Ic = I2 sin 2(wt + 240) = I2 sin (2wt - 120)
In = Ia + Ib + Ic = I2 {sin (2wt) + sin (2wt + 120) + sin (2wt - 120)} = 0
This is true in the same way for all even harmonics.
For 3rd and all multiples of 3rd Harmonic components:
For 3rd harmonic currents, the return currents from each of the three phases are in phase in the neutral and so the total 3rd harmonic neutral current is the arithmetic sum of the three individual 3rd harmonic phase currents.
Mathematically,
Ia = I3 sin 3(wt) = I3 sin (3wt)
Ib = I3 sin 3(wt - 120) = I3 sin (3wt - 360) = I3 sin (3wt)
Ic = I3 sin 3(wt + 120) = I3 sin (3wt + 360) = I3 sin (3wt)
In = Ia + Ib + Ic = I3{ sin (3wt) + sin (3wt) + sin (3wt)} = 3I3 sin (3wt)
This is true in the same way for all multiples of 3rd harmonics.
-MS
Reply Good Answer (Score 4)
09/05/2024 3:51 AM
  • Each individual phase has one wobble per cycle, 120deg apart from those on the other two phases.
  • There are three phases, each referenced to neutral.
  • Therefore there are three times as many wobbles on the neutral as there are on each individual phase, as each phase's wobbles will appear on the neutral simultaneusly.
Ergo third harmonic will be present on the neutral. Simplesζ.