DOL or Star Delta?

08/30/2010 1:25 AM

Dear Friends;

I am working for changing an old wound rooter variable speed motor (10KW, 400V) of a BOBST die cut machine with an AC Eddy current motor (15KW usually call VS motor) due to some problems in old motor. As we know that such motors have a built-in magnetic clutch. First we start the main motor then increase the amount of DC voltage to winding of clutch. I am confused about staring of that 15KW motor. I want to start it through DOL starter instead of Star delta as we have a strong power supply system and no voltage dip problem is expected. Can any body help me out? is their any rule of thumb that what is the max rating of motor which can be start through DOL?

__________________
Don't assume any thing, always check/ask and clear yourself
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Associate
Engineering Fields - Electrical Engineering - New Member

Join Date: Jun 2010
Location: IEC Domain
Posts: 43
#1

Re: DOL or star delta

08/30/2010 1:43 AM

Normally we use DOL starting on motors ranging from 1HP to 15HP (+- 5% difference factor). Star Delta (16HP-30HP). Motors bigger than that are either soft started or VSD are used. Every one has had different experience with starting techniques I've told you mine.

Hope it Helps

Regards,

DG EE

__________________
The Crazy Man Talks and The Smart Man Understands
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#2

Re: DOL or star delta

08/30/2010 1:56 AM

My understanding so far is that ALL motors (squirrel cage) are capable of being started DOL. It is only the utility restrictions that make one use reduced voltage starting. i am open to correction by some motor experts on this.

You have a wound rotor motor. These being more expensive, are generally used where torque and/or speed control is required. If this is the case, you would need a slip-ring motor starter i think.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: DOL or star delta

08/30/2010 3:16 AM

The motor will effectively be starting off load due to the clutch.

Go for DOL.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User

Join Date: Aug 2007
Location: Lahore
Posts: 369
#4

Re: DOL or star delta

08/30/2010 4:00 AM

OK. It mean the motor can be started through DOL without any fear. But we have other machines in which even a 11KW Eddy current motor has star delta starter. I think their is not a RULE OF THUMB for such kind of applications; it depends upon many other parameters such as, start up time of motor, distribution board capacity, rating of cables etc.

Am I right?

__________________
Don't assume any thing, always check/ask and clear yourself
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5
In reply to #4

Re: DOL or star delta

08/30/2010 7:14 AM

You say you have a strong power supply but then call in to question the distribution board supply and cabling.

I'm afraid it's a case of you have the information, we don't, it's got to be your decision.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#6
In reply to #4

Re: DOL or star delta

08/30/2010 10:46 AM

Please note that when you start a high capacity motor DOL, the system voltage drop does affect other loads connected to the same line/bus. However, there would be legal restriction by the Utility Company, only when you draw power from LT Lines from the Utility, because in such a case, the voltage drop caused by your DOL starting would affect your neighbour's electrical loads, thus making it a social problem. Please consult your local Utility Company for this limitation.

If you draw power from a HT Line, the voltage drop to your HT neighbour would be negligible under the same conditions. So, there would not be and there cannot be any legal restriction by the Utility in this case as to the maximum capacity of the motor that can be started DOL.

In this case, it is the user's electrical enginner who would decide the maximum capacity of the motor that can be started DOL, duly taking into account the effect of such starting on other loads connected to his LV Bus.

I have even commissioned may high capacity motors as high as 150 HP DOL on LV.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7

Re: DOL or Star Delta?

08/30/2010 11:52 AM

The "rule of thumb" is different for every installation and every jurisdiction, there is no universal rule that can be applied. Most likely your local utility may impose a rule, but even that can have exceptions; those rules typically are enforced only when nobody wants to take the time and effort to look at the starting profile in depth.

If you have S-D starters on motors as small as 11kW, that may be an indicator that your local utility has a rule like that. But it also may just mean that suppliers don't want to bother thinking about it and just supply S-D starters as a matter of course just in case.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Active Contributor

Join Date: Nov 2009
Location: Mumbai
Posts: 17
Good Answers: 1
#8

Re: DOL or Star Delta?

08/30/2010 11:02 PM

Its not just about Voltage dip problem that one should be worried about while using DOL. What about the inrush current? What about increased maintenance? What about motor windings? These are some of the questions that one should be considering. I have seen DOL being used for even 100 HP+ motors - but NOT recommended at all. However for a 15 kW motor - it is just a borderline case. In fact Y-D would be a better bet. The problem with Y-D would be Transients, Jerking - but should be just about ok for this motor size.

__________________
Cheers, RRV
Register to Reply
Anonymous Poster
#9

Re: DOL or Star Delta?

08/31/2010 12:48 AM

DOL Starter - Starting Current 5 to 7 times full load current of the delta connected motor.(It can be used upto (30 H.P)

Star Delta Starter- Starting Current 1.732(root 3) times of full load current of the motor. It can be used in the range of (30 H.P to 100 H.P)

For Exmple: Considered 50 H.P motor

By DOL starter its starting current is around 200AMPS

By Star Delta its starting current is around 75 AMPS

Register to Reply Off Topic (Score 5)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#10
In reply to #9

Re: DOL or Star Delta?

08/31/2010 5:07 AM

i am afraid that the starting currents will be more than these.

Normal full load current of a 50HP motor @ 415V 3 φ ≈ 83A

Starting current DOL ≈ 500A

Starting current ΥΔ ≈ 170A

Starting current ΥΔ = 1/3 X starting current DOL.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.