Our plant has 2MW running load. Our local power supply company charges a very huge amount if the load is increased beyond 2MW. They call that type of load as MDI. Can any body explain what MDI stands for?
Re: What MDI stands for?
08/30/2010 2:17 AM
in my location it is MDA Maximum Demand Allowed
not sure for the I
dont say it, write it
Good Answers: 181
08/30/2010 3:24 AM
If you are getting charged for exceeding your DMA then there's 2 ways forward.
1/ Re-negotiate the companies Maximum Demand
2/ Automatic load shedding when MDA is approached
2 involves some quite complex metering arrangements and shedding load may cause problems with your process.
08/30/2010 4:02 AM
Yes. It is MDA "Max Demand Allowed" not MDI.
09/26/2010 6:22 AM
Remove some load from the connected meter and obtain a separate meter for it or use a genset for that excess load
pnaban
08/30/2010 9:27 AM
MDI= maximum demand indicator.
It will show your plants maximum load (KW) and if it exceeds your sanctioned load, you are in for a penalty as per most of the regulatory acts, even if your average load (based on KWH or MWH are well within the sanction)
Good Answers: 804
Re: What Does MDI Stand For?
08/30/2010 12:21 PM
Maximum Demand current, with current being shown by its SI notation "I", perhapse?
08/31/2010 3:21 AM
Mild Dose of Influenza?
Reply Score 2 for Off Topic
09/02/2010 12:40 PM
MDI Stand for (Maximum demand Indicator) when u taken cpower connection from any company thay asked about your peek load and u r limted to use power under your maximum demand, so you may contact again to company and change your maximum demand again, and installed in your factory energy meter with MDI system which will indicate about your load so u can control your panalty,