Effect of Short Circuit Current on Electric Panel or Switchgear

08/30/2010 2:16 AM

Dear Sir,

Hello

I am a power electric engineer. I want to know about the effect of short circuit current on copper cross section choosing in electric panel and/or switchgear.

Thanks, H. Masjedi

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: ELECTRIC POWER

08/30/2010 3:35 AM

Conductor size must take in to account electro-mechanical and thermal stresses imposed by a short circuit.

You can reduce the electro-mechanical stress by increasing the number of supports but then this increases the thermal stress.

It's time for a juggling act.

__________________
The reports of my death are greatly exaggerated.
Reply
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member Popular Science - Genetics - New Member Technical Fields - Technical Writing - New Member Safety - ESD - New Member Engineering Fields - Power Engineering - New Member

Join Date: Jul 2010
Location: INDIA MUMBAI
Posts: 67
#2
In reply to #1

Re: ELECTRIC POWER

08/30/2010 8:21 AM

A short-circuit results in an excessive current due to low impedance of the faulty circuit between the source of supply and the fault. This excessive current causes excessive heat (= IC', . R) in the current-carrying conductors and generates electromagnetic effects (electric field) and electrodynamic forces of attraction and repulsion between the conductors and their mounting structure. These forces are distributed uniformly over the length of conductors and cause shearing forces due to the cantilever effect as well as compressive and tensile stresses on the mounting structure. The effect of a short-circuit therefore requires these two very vital factors (thermal effects and electrodynamic forces) to be taken into account while designing the size of the current-carrying conductors and their mounting structure. The latter will include mechanical supports, type of insulators and type of hardware, besides the longitudinal distance between the supports and the gap between phase-to-phase conductors.

__________________
Correct Me If Iam Wrong, Suggestions/Recommendations needs to be verified before implementation
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: Effect of Short Circuit Current on Electric Panel or Switchgear

08/30/2010 10:37 AM

Why don't you attend to our training programme on Electrical Design of Switchgear Assembly?

Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#4

Re: Effect of Short Circuit Current on Electric Panel or Switchgear

08/30/2010 11:44 PM

Since you have asked for effect of short circuit,

During short circuit in the switch board, there will be

1)Electro - dynamic forces acting on the busbars

2) Temperature of busbars,current carrying elements will get increased.

If the Switch board is designed to withstand a particular short circuit current for a particular time, the switch board will withstand and there will not be any failure.

If the short circuit current and time of fault are greater than the designed values the switch board will fail ( Blast into pieces)

__________________
Ramesh,Freelance Electrical/automation Consultant
Reply
Anonymous Poster
#5

Re: Effect of Short Circuit Current on Electric Panel or Switchgear

09/07/2010 1:53 AM

Who appointed you as a Power electric engineer?

Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6
In reply to #5

Re: Effect of Short Circuit Current on Electric Panel or Switchgear

09/13/2010 8:36 AM

Good question?

Just hope I'm not around to find the answer

__________________