I was told if we improve PF will also energy saving, example if exisiting PF is 0.92 and we increase the capacitor to 0.98. We are saving of 6% of total Kwh monthly.
.98 is a very high PF to achieve, not impossible but expensive. Aim for .95.
If the plant loading is constant go for static PF correction, otherwise variable PF correction is available.
A form of variable PF correction would be to fit static capacitors to selected large drives, as the drive starts additional correction is introduced. It's an old way of doing it but tried and tested.
Unfortunately it all comes down to money, you've got to spend to save.
__________________
The reports of my death are greatly exaggerated.
In first
case, PF corrects at the load by connecting capacitor at motor terminal. In
this way, we provide reactive power of load at the spot and the reactive current
components don't pass in the motor input cable and thus we save I²R losses from
motor to transformer.
In second
case, PF corrects at main distribution board by connecting a PF controller and
capacitors. In this way, reactive current components of load passes through main
supply cable from distribution board to load which increases I²R losses as
compare with 1st case.
But if don't
correct PF, these I²R losses increases as transformer/generator has to provide
both active and reactive current components to load. These reactive current components
starts from source to load increase our electricity bill but not 6%. It is a
little amount.
May some power expert correct me and you.
__________________
Don't assume any thing, always check/ask and clear yourself
From the fact you had a PF of .92 some correction had to be in place. You made no mention of I²R losses. If this is the loss your concerned with then say so.
Increase the static correction in the distribution network.
By improving the pf from 0.92 to 0.98 you are decreasing the current by about 6% (0.92/0.98=0.939)
But then the loss is depending upon the I2 and not I and a 6% reduction in I will have about 11% in I2.
But then this is applicable for the resistive portion of the circuit between the compensator and the source
Let us assume your source is the utility transformer. at a distance of say 150mt from it you have the compensator put and at 10mt from it is the load.
In this case you must neglect the 10mt and the load since those are least bothered about the compensator.
It is the 150mt that will bear any improvement and that will be negligible since it is only the cabling and will have (or if properly designed should have) very low resistance and will save you a few watts only.
Unless you are working at very high power and currents, I don't really find any significant improvement in 0.92 to 0.98.
Of course for low pfs say 0.8 or even 0.85 it might be worth a try.
The concept of energy savings with PF improvement are almost always a scam,intended to separate the ignorant masses from their money. The fact that someone has told you that an improvement from very good PF to nearly impossible PF will save you that much energy is evidence that this is in fact a scam, do not fall for it. By the way, take no offense to my reference of ignorant masses, there is no shame in being ignorant if you have no previous knowledge of something. Not everyone can be an electrical engineer with training to understand this obscure issue, which is exactly what the scammers are counting on.
Power Factor improvement will, at best, save MONEY, BUT ONLY IF YOUR UTILITY PENALIZES YOU FOR POOR POWER FACTOR. If you have an industrial or large commercial installation
that may be the case, but if you are thinking this will have an effect on a
residential power bill, you are mistaken. The vast majority of utilities in the
world assess no penalties for poor power factor on residential customers. None.
There is a very very tiny amount of losses in the conductors that can be saved by locating a PF correction capacitor AT THE OFFENDING DEVICE, but an overall (bulk) capacitor will do nothing in that area.
__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
This has been discussed many times in this forum. However, again JRaef explained it nicely. GA.
- MS
__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Quote Aikhh "I was told if we improve PF will also energy saving, example if exisiting PF is 0.92 and we increase the capacitor to 0.98. We are saving of 6% of total Kwh monthly."
Since pf ≠ kWh, then you can be certain that what you heard is a LIE.
Your equipment will consume EXACTLY the SAME energy at ANY power factor, and the kWh meter will not see a difference either.
The only claimed savings that has any basis in reality is related to heat in the conductors by the formula I2R, where I is the current and R is the resistance. What that means is, that even if you did see a magical 6% reduction in your current, the resistance value planned into most circuits with proper wiring is almost ZERO.
The math then; {(your original amps) - (your adjusted amps)}2 X zero = zero (rounded to the nearest 1,000th).
Go ahead, touch a nearby cord or two and see if you can detect any heating. Most cords will in fact feel quite cold when properly sized. If you are not challenging a conductor's capacity, neither you or your meter will notice anything. Only under overloaded conditions for your conductor might you begin to notice any heating.
In many places, ice forming on power lines in the winter pulls them down causing outages etc. There isn't enough I2R heating in properly sized conductors that feed entire neighborhoods to pay for whatever device someone is trying to claim will benefit you from the claimed "6%" of your tiny (by comparison) load.
Again, 6% pf improvement does not equal 6% kWh improvement. Any claim that it does is a flagrant lie.
Regards, CJM.
__________________
I do not 'know it all', but i will admit that I would like to. CJM
If you use bulk(automatic) compensation connected to the Switchboard there will be a small saving which depends on the resistance of the main cable and the magnitude of the current consumed from the utility.
If you use static capacitors to motors above ,say,5hp the current consumed by each motor connected to a capacitor will be reduced and in some cases smaller cables could be used.The savings will be more but selection of capacitor should be done by a prefessional.