Heat Trace - Correct RTD Placement

08/30/2010 1:13 PM

Hello,

I am new to heat trace design, trying to learn more about it. I am interested if there is a guide anywhere that describes correct RTD placement, or if it is just a rule of thumb thing. Any help/information will be useful thanks.

~Hubbard

Register to Reply
Pathfinder Tags: Heat Trace
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#1

Re: Heat Trace - Correct RTD Placement

08/30/2010 3:32 PM

Are you heating the pipe/vessel for freeze protection or to maintain product temperature?

How you answer will dictate where you mount the RTD.

For freeze protection, mount the RTD to detect un-adulterated ambient temperature.

To maintain product temperature, mount RTD on pipe/vessel.

You can also call the HT manufacturer or manufacturers rep. They are usually very helpful in pointing you in the right direction.

This link is very limited and generalized: http://www.tycothermal.com/assets/NorthAmerica/English/Documents/Installation_Operation_and_Maintenance_Manuals/Products/476/H56998_RTD200_II_0203.pdf

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply
Member
Engineering Fields - Power Engineering -

Join Date: Aug 2010
Location: Midwest, currently living in Denver, CO
Posts: 9
#2

Re: Heat Trace - Correct RTD Placement

08/30/2010 3:44 PM

Thanks, I am concerned with freeze protection on pipes currently. Is the RTD mounted on the pipe or near the pipe? The link you provided showed the RTD with a lead wire, does this run back to the power kit or to the controller? I do not have a vendor, as I said I'm just a student of heat trace for now. Thanks.

Register to Reply
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#3
In reply to #2

Re: Heat Trace - Correct RTD Placement

08/30/2010 4:08 PM

Hubbard,

As stated in my previous reply, for freeze protection mount RTD where it can detect un-adulterated ambient temperature (EDIT) where freeze protection is desired.

If you have a controller, run an RTD extension lead back to the controller as well as the power connection kit leads (power).

If no controller, you can run the RTD lead to the power connection kit provided the kit has an RTD input. Some power connection kits come with an integral RTD (depending on manufacturer) at which point you do not need a separate RTD (in fact this type usually comes with an armor covered RTD to protect the RTD from damage).

Hopefully you are aware that you CAN NOT connect the RTD element directly to heat trace line voltage to control it.

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply
Member
Engineering Fields - Power Engineering -

Join Date: Aug 2010
Location: Midwest, currently living in Denver, CO
Posts: 9
#4
In reply to #3

Re: Heat Trace - Correct RTD Placement

08/30/2010 4:18 PM

KJK/USA,

Thank you for your reply. Yes I am aware that you cannot connect the RTD element directly to heat trace line voltage to control it.

I am also aware that you need to put the RTD in a place that will be useful in determining the ambient temperature around the pipe you are considering.

Does there need to be a minimum distance between RTDs or is it dictated only by circuit length? Is only one RTD needed per freeze circuit? Are the RTD's typically placed at the end or the beginning of the circuit (say they are within 100 feet of each other) or does it matter? I see they are fed by conduit. Are the RTD's typically mounted on a wooden apparatus near the pipe? I'm guessing they are not mounted on anything metal as that would probably interfere with a correct temperature reading?

~Hubbard

Register to Reply
3
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#5
In reply to #4

Re: Heat Trace - Correct RTD Placement

08/30/2010 4:39 PM

Hubbard,

You can specify to the manufacturer that you need an outdoor RTD. These are usually armor covered to protect the RTD from the environment in which it is mounted.

These typically come with a metal bracket (which will not effect the RTD reading the ambient temp).

As far as mounting, generally, the closer to the power connection kit the better (even if it is fed to a controller somewhere else).

Typically it is one RTD per heating zone. You also must take into consideration the length of the cable run to calculate your amperage.

You will need the line run amperage to ascertain the size of the power connection kit with integral RTD or size of contacts within the controller.

I don't mind helping you but you really need to contact the manufacturer that you are purchasing your particular heat trace system from as there are variables from manufacturer to manufacturer. Most if not all of them will help you out with manufacturer specific information.

Good luck with your heat trace project>

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply Good Answer (Score 3)
Member
Engineering Fields - Power Engineering -

Join Date: Aug 2010
Location: Midwest, currently living in Denver, CO
Posts: 9
#6
In reply to #5

Re: Heat Trace - Correct RTD Placement

08/30/2010 4:44 PM

KJK/USA,

Thank you for the information. I have not done a heat trace project myself but I think the technology is interesting. I am learning in case I decide it is something I would like to get into. Usually when you are on a project you do not have time to figure out these little details. It is good to know the vendors are so willing to help with design.

Regards,

~Hubbard

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#7
In reply to #5

Re: Heat Trace - Correct RTD Placement

08/30/2010 6:02 PM

You deserve an "atta boy" for this one.

Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#8
In reply to #7

Re: Heat Trace - Correct RTD Placement

08/30/2010 7:05 PM

Seconded! Remarkable restraint.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Off Topic (Score 5)
Guru
Safety - Hazmat - New Member Safety - ESD - New Member Engineering Fields - Transportation Engineering - New Member Popular Science - Evolution - New Member Technical Fields - Procurement - New Member Hobbies - Target Shooting - New Member Popular Science - Cosmology - New Member Engineering Fields - Architectural Engineering - New Member Technical Fields - Marketing/Advertising - New Member Engineering Fields - Food Process Engineering - New Member

Join Date: Dec 2005
Location: Mariposa Ca
Posts: 5800
Good Answers: 114
#13
In reply to #8

Re: Heat Trace - Correct RTD Placement

08/31/2010 12:51 AM

I think you guys may have been a little harsh Here

I would assume that RTD's are similar to 2 wire thermocouples. some controllers are going to require ungrounded units, others more forgiving. From what I know most RTD's are 3 wire, using a resistor to stabilize the output. I know when I worked at the bakery, we actually got longer service using Bi-metal thermocouple wire twisted together, instead of bayonet mount J-type. This had more to do with the ability to visually assure good contact with a large chunk of hot metal

Were I doing heat trace to keep pipes from freezing I would stick with the self regulating stuff.

At least Hubbard bothered to register & login

Register to Reply Score 1 for Good Answer
Member
Engineering Fields - Power Engineering -

Join Date: Aug 2010
Location: Midwest, currently living in Denver, CO
Posts: 9
#16
In reply to #13

Re: Heat Trace - Correct RTD Placement

08/31/2010 9:24 AM

Thank you Garthh.

My speciality is in Cathodic Protection, but what I have learned so far about RTDs, I would agree with what you have described.

I will take into consideration what you recommended about the self regulating HT. Thanks again.

Register to Reply
Member
Engineering Fields - Power Engineering -

Join Date: Aug 2010
Location: Midwest, currently living in Denver, CO
Posts: 9
#9

Re: Heat Trace - Correct RTD Placement

08/30/2010 7:09 PM

Yeah, thanks alot, you pompus a$$es.

Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#10

Re: Heat Trace - Correct RTD Placement

08/30/2010 7:14 PM

Hubbard,

I'll respond to your PM here.

Oh well. Didn't see post #9 till just now. I'll just erase my response to your PM.

Have a great day.

Register to Reply Off Topic (Score 5)
Member
Engineering Fields - Power Engineering -

Join Date: Aug 2010
Location: Midwest, currently living in Denver, CO
Posts: 9
#11
In reply to #10

Re: Heat Trace - Correct RTD Placement

08/30/2010 7:19 PM

Does it matter? Just because I don't have a current practical application doesn't mean I will never do a heat trace design.

I don't see anything saying this is a forum just for people doing actual work in lieu of wanting information. You can't do an actual design until you learn how in the first place.

Seeking academic knowledge is a waste of others' time? Good to know. I'll make sure to qualify the question next time.

Register to Reply
2
Power-User

Join Date: Nov 2009
Posts: 335
Good Answers: 63
#12

Re: Heat Trace - Correct RTD Placement

08/30/2010 8:45 PM

The process heat tracing that I've done is all central controller controlled with pipe mounted RTD's. I suspect that thermostatic 'freeze protection' designs with an ambient thermostat have an integral temperature sensor as part of the controller (temp switch).

I do remember installing a single ambient sensor that the central controller used as an anticipator, where the controller would call for heat quicker than might be expected if the only control were the pipe mounted zone sensor when the ambient temp was dropping.

I've always used the clamp-on style RTD's like this, where the mounting pad gets clamped to the pipe with a strap:

Pyrotenax's installation instructions are valid:

"Where flow and static conditions occur within one heating zone, the temperature
sensor should be located at a point of no flow and away from the end of the pipe or a heat sink such as a pipe support."

A heat sink's temperature can be unrepresentative of the process temperature, as can regions of no flow (dead heads).

"The temperature sensor should be strapped in good thermal contact with the pipe and protected so that insulating materials cannot become trapped between it and the heated surface."

Thermon has a diagram for location of the sensor on the pipe:

Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14

Re: Heat Trace - Correct RTD Placement

08/31/2010 3:12 AM

An RTD requires a transmitter, cabling, a power supply, a trip-amplifier and a contactor to switch the trace heating on and off.

Self-limiting trace heating tapes don't require temperature sensing and switching. They stay on all the time and the power load is self-regulated to maintain the desired temperature.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Member
Engineering Fields - Power Engineering -

Join Date: Aug 2010
Location: Midwest, currently living in Denver, CO
Posts: 9
#15

Re: Heat Trace - Correct RTD Placement

08/31/2010 9:19 AM

Thank you both very much for your helpful comments.

Carl E, the diagram that you provided really lays it out for me, thanks.

Register to Reply
Participant

Join Date: Sep 2010
Posts: 4
#17

Re: Heat Trace - Correct RTD Placement

10/13/2010 12:51 PM

Normally you put RTD where there is no temperature interferences which could be caused by other heat sources, or heat sinks such as pipe supports, valves, etc.

Register to Reply
Register to Reply 17 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Canterburian (1); Carl_E (1); Garthh (1); Hubbard (7); JohnDG (1); KJK/USA (3); lyn (2); PWSlack (1)

Previous in Forum: Two Phase Input Three Phase Output Transformers   Next in Forum: Important BS List - Add Your Names

Advertisement