Dear all,
Conductor short circuit current offered by different manufacturers like 0.16,0.172,0.156 kA/sec. Which conductor is better lower value or bigger value? Any one can suggest for me
K. Senthil
Re: short circuit current
09/02/2010 6:14 AM
What is the application?
09/02/2010 6:33 AM
Ita a LT control cable for instrumentation purpose
09/02/2010 7:48 AM
The answer doesn't need any thinking at all if you use your logic little bit:
The bigger one is the best-less Resistance.
Good Answers: 181
Re: Short Circuit Current
09/02/2010 8:40 AM
I'm trying to get my head around conductor short circuit currents when applied to a control cable, why didn't you just look at ohms per metre.
It would be one hell of a control system if you've got to start worrying about fault currents in KA
09/07/2010 1:46 AM
The values you given are all wrong....reconfirm it first.
Good Answers: 170
09/11/2010 10:29 PM
Obviously the higher the SC Withstand, the better. But perhaps you could be oversizing the cable in that case. Please do a fault level calculation study and select the cable with a nearest higher SC withstand capacity.