Three Phase Generator

09/05/2010 8:13 AM

hi,

can some one pls help me on this

there is three phase ac generator dual voltage 230v/380v, there is no marking on the 12 leads of the generator but it looks connected on low as each phase has two cables connected to it.

now if i will connect it on high voltage 380v, for example phase 1, i dont know which is lead no:1,4,7,10. so can i connect these two coils on series without looking if terminal no 1 is the live side and terminal 7 is connected to terminal 4.

in other words: does it matter if coil with terminals 1,4 will be at the live side or neutral side and same for the coil with terminals 7,10?

hope you understand what i mean.

thanks for your help

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: three phase generator

09/05/2010 8:41 AM

hope you understand what i mean

Not realy but try this

Phase1 coil 1 terminals 1&4 coil2 terminals 7&10

Phase2 coil 1 terminals 2&5 coil2 terminals 8&11

Phase1 coil 1 terminals 3&6 coil2 terminals 9&12

For higher voltage connect

4 to 7

5 to 8

6 to 9

Neutral 123

L1 out 10

L2 out 11

L3 out 12

__________________
The reports of my death are greatly exaggerated.
Reply
Anonymous Poster
#2
In reply to #1

Re: three phase generator

09/05/2010 10:18 AM

hi, thanks for your reply.

the problem here that there is no marking on the wires and i dont know which is 1 or 2 or ....etc

on each phase there are two coils connected on parallel thats why i thought it connected on low voltage, now to connect on high i need to make each two parallel coils on series.

does it matter if i just make the two parallel coils to series connection without looking if it is connected for example 4 to 7 or 4 to 10, 1 to 7 or 1 to 10?

thanks

Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#3
In reply to #2

Re: three phase generator

09/05/2010 12:06 PM

You can test this easily:

Disconnect one coil and connect in series. You might end up with double the voltage or about zero?

__________________
Plenty of room here
Reply
Anonymous Poster
#4
In reply to #3

Re: three phase generator

09/05/2010 2:34 PM

hi

thanks for your help, i will try this.

Reply
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#6
In reply to #3

Re: three phase generator

09/06/2010 4:18 AM

It is correct that you end up with double voltage or nothing. But with this test you find the connention between terminals 4/7 and 5/8 and 6/9. But you still not know

  • which lead is lead number 1 or 10
  • which lead is lead number 2 and 11
  • which lead is lead number 3 and 12

To solve this, you have to make a random connection for the "start" and the "ends" of each phase in a wye point. If it is not the correct way there are only 4 possiblities to connect the wye point. Just try them all.

Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Three Phase Generator

09/06/2010 3:27 AM
  • Which manufacturer?
  • What model?
  • Where is the manual?
  • Where is the telephone?
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#7

Re: Three Phase Generator

09/06/2010 12:30 PM

As Tonys suggested:

To find the ends start by looking at the ends that are put together for Neutral, in the existing configuration (Low voltage parallel). These will be your 1,2,3 and 7,8,9

Now every output phase had 2 ends: 4,10 ; 5,11 ; 6,12

By separating them one phase at a time, you will be able to identify which is which coil.

Reply
Anonymous Poster
#8

Re: Three Phase Generator

09/07/2010 8:51 AM

guest; if you have ring terminals on the end of the leads, check them for the numbers. perry

Reply
Reply to Forum Thread 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); dvmdsc (1); LAA_Lucke (1); PWSlack (1); rudy.leurs (1); TonyS (1)