Power Factor Improvement - Diesel Generator

09/06/2010 6:33 AM

We have 60kw diesel generator installed in factory.Over all PF of load on generator is 0.65.Want to improve it to o.8 .Can anyone suggest effective size of capacitor bank & place of connection?

__________________
Expand horizons thru' knowledge sharing
Register to Reply
Pathfinder Tags: Power Factor Improvement
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User
India - Member - Justin Anto Engineering Fields - Electrical Engineering - Marks never made me laugh, but good memories did

Join Date: Sep 2010
Location: Thrissur, Kerala, India
Posts: 177
Good Answers: 3
#1

Re: Power Factor improvement_Diesel Generator

09/06/2010 6:42 AM

At which pf, it can deliver 60KW (it may be there in name plate) or you have to give the KVA rating.

__________________
If you can't find a way, make one........
Register to Reply
Member

Join Date: Sep 2010
Location: Pune,Mumbai,India
Posts: 5
#2
In reply to #1

Re: Power Factor improvement_Diesel Generator

09/06/2010 7:04 AM

Its 62.5KVA / 50 KW generator & not 60 kw as mentioned earlier.

__________________
Expand horizons thru' knowledge sharing
Register to Reply
Power-User
India - Member - Justin Anto Engineering Fields - Electrical Engineering - Marks never made me laugh, but good memories did

Join Date: Sep 2010
Location: Thrissur, Kerala, India
Posts: 177
Good Answers: 3
#3
In reply to #2

Re: Power Factor improvement_Diesel Generator

09/06/2010 7:26 AM

Use 3 x 5KVAR capacitor panel and connect it as star or delta according to generator output winding connection.

__________________
If you can't find a way, make one........
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4
In reply to #2

Re: Power Factor improvement_Diesel Generator

09/06/2010 7:39 AM

For such a small machine is it worth the expence?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User
India - Member - Justin Anto Engineering Fields - Electrical Engineering - Marks never made me laugh, but good memories did

Join Date: Sep 2010
Location: Thrissur, Kerala, India
Posts: 177
Good Answers: 3
#5
In reply to #4

Re: Power Factor improvement_Diesel Generator

09/06/2010 7:48 AM

He may not needed full load at all time....

No problem if it is a 3 x 3 KVAR capacitor bank.

What is your suggestion?

__________________
If you can't find a way, make one........
Register to Reply
Member

Join Date: Sep 2010
Location: Pune,Mumbai,India
Posts: 5
#7
In reply to #5

Re: Power Factor improvement_Diesel Generator

09/07/2010 12:11 AM

Dear Justin,Thank you for immediate response. We have loaded the generator to 40 KW(80% of gen capacity).Hence after starting it, within half an hour its stops due to Alternator overloading / overheating.when checked ,we found the overall PF of factory load is 0.65/0.68.We need to improve this to 0.8 ,for which alternator is designed.

__________________
Expand horizons thru' knowledge sharing
Register to Reply
Power-User
India - Member - Justin Anto Engineering Fields - Electrical Engineering - Marks never made me laugh, but good memories did

Join Date: Sep 2010
Location: Thrissur, Kerala, India
Posts: 177
Good Answers: 3
#8
In reply to #7

Re: Power Factor improvement_Diesel Generator

09/07/2010 1:01 AM

1) Whether your system is using varying power? (It was not mentioned in the question). If the power consumption is varying you can not use a fixed pf compensator. Real time compensator is available now. (With PWM technology)

OR

2) Try to find out which machines are working with low pf and how much VAR it needs, and give compensation with that machine. (Ignore machines with small ratings)

Also don't start your generator when capacitor is connected. Start capacitor only after DG is started.

If your need is 40KW you have to supply around 6KVAR only. KVAR requirement will vary with power requirement.

__________________
If you can't find a way, make one........
Register to Reply
Participant

Join Date: Jul 2010
Location: Bahrain
Posts: 2
#14
In reply to #8

Re: Power Factor improvement_Diesel Generator

09/07/2010 4:51 AM

I agree with above comments from others about installing a Capacitor Bank is not a Cost effective solution when compared to the load. "If your need is 40KW you have to supply around 6KVAR only. KVAR requirement will vary with power requirement." as stated above How did you arrive at 6KVAr for a 40KW load i believe you would require nearly 13~17KVAr capacitor bank.

Register to Reply
Power-User
India - Member - Justin Anto Engineering Fields - Electrical Engineering - Marks never made me laugh, but good memories did

Join Date: Sep 2010
Location: Thrissur, Kerala, India
Posts: 177
Good Answers: 3
#18
In reply to #14

Re: Power Factor improvement_Diesel Generator

09/07/2010 6:22 AM

Sorry, typing error.....

I meant 16 KVAR.

__________________
If you can't find a way, make one........
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#20
In reply to #18

Re: Power Factor improvement_Diesel Generator

09/07/2010 12:21 PM

50kW at 0.8 pf needs 62.5kVA and kVAr = 37.5

AT 0.65 pf the kVAr = 47.5

To rectify to 0.8, you need to produce (47.5-37.5) = 10kVAr in 3 phase supply. Which means that each phase will need 10/√3 = 5.8 ~ 6kVAR

YOU WERE CORRECT!

Register to Reply
Associate

Join Date: Mar 2009
Posts: 51
Good Answers: 4
#23
In reply to #20

Re: Power Factor improvement_Diesel Generator

09/08/2010 2:36 AM

it was calculated for 40KW we are getting nearly 16.76 KVAR. normally KVAR is mentioned for a 3 PHase, i dont know how single phase KVAR is mentioned for a 3 phase load.

If we calculate:

KVAR = KW(Tan(P.f present) - tan (P.f to be achieved))

= 40 (tan(cos-1(0.65) - tan (cos -1 (0.8)))

= 40 (1.169- 0.75) = 40 * 0.419 = 16.76 KVAR required to increase the PF from 0.65 to 0.8 for a 40KW load.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#26
In reply to #23

Re: Power Factor improvement_Diesel Generator

09/08/2010 8:04 AM

Sorry, you are correct!

I kept the same KVA in my calc...

Register to Reply
4
Power-User

Join Date: Nov 2009
Posts: 198
Good Answers: 18
#9
In reply to #7

Re: Power Factor improvement_Diesel Generator

09/07/2010 2:07 AM

You are running such a small "consumer", to control Pf correctly you will need a Pf contoller. The cost of this is quite high and wont show you much savings. First find out which motor (or more) in your plant consumes the most energy. Then find the correct caps to connect at the motor or motors.You connect them after your switchgear alongside or at the motor.( you may also connect at contactors in panel) This way you will only use caps where needed WHEN needed. You were given a Rating for your entire plant, a lot of which may be lighting or non-inductive loads, in which case you are over compensating and may create more problems than is worth the effort.

__________________
Always learning
Register to Reply Good Answer (Score 4)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#11
In reply to #9

Re: Power Factor improvement_Diesel Generator

09/07/2010 2:46 AM

This is the solution I would go along with. The correction only comes in as required. Automatic correction is far to expensive for such a small installation.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#12
In reply to #11

Re: Power Factor improvement_Diesel Generator

09/07/2010 4:00 AM

Thinking about it, it would be cheaper to purchase a new generator than automatic PF correction.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Anonymous Poster
#6
In reply to #4

Re: Power Factor improvement_Diesel Generator

09/06/2010 8:03 AM

I agree with TS. The cost will easily outweigh the benefits.

However for a factory 50KW looks to be very small (are you sure about it?)

For the compensator, if you insist, find out the culprit (the low pf equipment) and put the bank near it.

Most likely it is a motor running at much lower than the rated load.

UD15

Register to Reply Score 1 for Good Answer
Anonymous Poster
#10

Re: Power Factor Improvement - Diesel Generator

09/07/2010 2:23 AM

What is your load which has 0.65 PF. Buy equipments/motors which has better power factor.

Register to Reply
Associate

Join Date: Mar 2009
Posts: 51
Good Answers: 4
#13

Re: Power Factor Improvement - Diesel Generator

09/07/2010 4:41 AM

I agree with above comments from others about installing a Capacitor Bank is not a Cost effective solution when compared to the load.

"If your need is 40KW you have to supply around 6KVAR only. KVAR requirement will vary with power requirement." as stated above

How did you arrive at 6KVAr for a 40KW load i believe you would require nearly 13~17KVAr capacitor bank.

Register to Reply
Power-User
India - Member - Justin Anto Engineering Fields - Electrical Engineering - Marks never made me laugh, but good memories did

Join Date: Sep 2010
Location: Thrissur, Kerala, India
Posts: 177
Good Answers: 3
#16
In reply to #13

Re: Power Factor Improvement - Diesel Generator

09/07/2010 4:55 AM

Sorry, typing error.....

I meant 16 KVAR.

__________________
If you can't find a way, make one........
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#15

Re: Power Factor Improvement - Diesel Generator

09/07/2010 4:53 AM

If you add to each load a small cap bank sized for that load, that is switched in and out as the load is switched in and out, there is no big deal. Also, nobody can make a mistake!!!

SIMPLE!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Score 1 for Good Answer
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#17
In reply to #15

Re: Power Factor Improvement - Diesel Generator

09/07/2010 5:45 AM

that is also the way I would try to fix it, so GA andy

Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#19

Re: Power Factor Improvement - Diesel Generator

09/07/2010 8:03 AM

Dear Ram Das,

Proposing of capcitor bank with power factor controller( for varying load ) is not economically viable for small size DG set.. Since in any factory/ industry about 70% of load is inductive; i.e; motors, gas dischrarge lamps, welding set, etc; it is better to installed capacitor across each inductive load for lagging VAR compensation. Also you may please check proper functioning of cooling system of DG set.

Regards,

Manindra

__________________
Manindra
Register to Reply
Member

Join Date: Sep 2010
Location: Pune,Mumbai,India
Posts: 5
#21
In reply to #19

Re: Power Factor Improvement - Diesel Generator

09/08/2010 1:21 AM

As suggested earlier, putting capcitor bank of 16 kvar & manually switching on after the generator start by placing the cap bank in switch gear control panel(main distribution board ) should solve the problem.Do everybody agree?

__________________
Expand horizons thru' knowledge sharing
Register to Reply
Power-User

Join Date: Nov 2009
Posts: 198
Good Answers: 18
#22
In reply to #21

Re: Power Factor Improvement - Diesel Generator

09/08/2010 2:22 AM

No, that was not the gist of it. You are supposed to ascertain where your "problem" machines/motors are. then, as ANDY pointed out again use caps only sized for that load, at the load. These caps will switch in everytime the load comes on, and they will be only big enough to take care of the reactive component on that particular macine. The way you are proposing is a totally manual system where you supply KVAr for your full load. Manually switching that bank is calling for overcompensating problems.

__________________
Always learning
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#24

Re: Power Factor Improvement - Diesel Generator

09/08/2010 3:04 AM

How many motors are there in your factory, and what size?

As jvrj said you're going to cause yourself more problems with over compensation if you switch the capacitors on after starting the generator. If you are determined to go down the road of a single capacitor bank then switch them in at about 60% of total load. If the load varies during the day you're going to get fed up of switching them on and off.

Go for single drive correction on say just 5 drives, you'll have to decide which. You know the machines.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User

Join Date: Nov 2009
Posts: 198
Good Answers: 18
#25
In reply to #24

Re: Power Factor Improvement - Diesel Generator

09/08/2010 5:00 AM

Well said and thanks Tonys, now if only the OP will heed this.

__________________
Always learning
Register to Reply
Participant

Join Date: Sep 2010
Posts: 4
#27

Re: Power Factor Improvement - Diesel Generator

09/08/2010 8:51 PM

What are your connected loads ? How many motors and what is their HP ?

Register to Reply
Register to Reply 27 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

amarnath.sn (2); Andy Germany (1); Anonymous Poster (2); edison (1); justinanto1987 (6); jvrj (3); LAA_Lucke (2); manindra (1); ram_das (3); rudy.leurs (1); sarvancv (1); TonyS (4)

Previous in Forum: Electrical Injuries   Next in Forum: Calculating Fault Level for Transformer

Advertisement