Can This Transformer be Used as a Step Up Transformer?

09/06/2010 10:44 AM

A Transformer having 33/6.6 kv 10 MVA rating can v use it as a step up Transformer with same rated power? If no then what is the difference between them???

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: Can This Transformer be Used as a Step Up Transformer?

09/06/2010 11:34 AM

Yes. The rating 33/6.6 KV doesn't indicate it is step down transformer, it only indicates its HV rating is 33 KV and LV side is 6.6 KV. A transformer itself is not designated as step-up or step-down unless it is used for these purposes. If the transformer's other ratings including the vector group serve the requirement, it is perfectly ok to use.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Associate

Join Date: Mar 2009
Posts: 51
Good Answers: 4
#2

Re: Can This Transformer be Used as a Step Up Transformer?

09/08/2010 4:04 AM

As Msamad said we can use any transformer for step-down or step-up unless the vector group, frequency and voltage matches, we have to also take care of the Tap changers in the transformer. it also plays a significant role to use.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: Can This Transformer be Used as a Step Up Transformer?

09/11/2010 9:45 PM

A transformer is a bi-directional device and your 33/6.6kV Step Down Transformer can very well be used as a 6.6/33kV Step Up transformer. But, there could be magnetising in-rush current problems while you charge the trafo from LV Side. Please underake a study of this. Also, take care about Vector Group, Earthing of Neutral, etc.

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#4
In reply to #3

Re: Can This Transformer be Used as a Step Up Transformer?

09/29/2010 1:01 AM

what about onload tapchanger which gets signal from secondary voltage and adjust taps by AVR to maintain a constant secondary voltage within limits?.

__________________
pnaban
Register to Reply