Sir,
Water transmission pipeline
The level measurement for horizontal Surge Vessels and concrete reservoirs
is implemented with SITRANS LR200 reflex radar type transmitters.
For level alarms at tanks and surge vessels the Siemens Pointek CLS 200, a high corrosion resistant capacitive rod type switch, are used.
We have 10 horizontal surge vessel 156m3 volume linked to each other of which we have #5 & #6 vessel as a reference. the instrument is mounted on top of the surge vessel #5 & 6. The air compressor inlet is given to each tank from top. The air compressor is provided with filters and dryers.
In 24 hours the level instrument works good for only 20 hours. And the rest time on SCADA it shows hardware fault because it is over-ranged to 116%. I re-calibrated the instrument from the software after this the instrument works fine for another around few hours then again the radar level instrument signal on SCADA is showing abnormal reading. I have calculated the nozzle of the surge vessel as this is a horn type instrument. I also investigated if there are any foreign material in the tank. As per our design the air compressor automatically starts when the water in surge vessel reach to 75%. the level suddenly jumps from 75% to 116%. Maybe I'm missing some point in my investigation. If you have any advice or suggestion would be a great help!
Thank You.