Hi
Can someone give any comments or idea about the grounding issue. I am doing the grounding study for 138 kV switching station. There is no transformer in the station. The calculated ground resistance using CDEGS software is 2.4 ohm. The fault current is 3kA. The measured ground resistance test in the field is 0.82 ohm. To investigate the difference between measured and calculated value, I found that one 120VAC line comes from outside single phase transformer to relay operating panel inside the substation with neutral. That neutral is connected to substation ground grid. The outside single phase transformer connected to 25 kV line and low side 120VAC goes to inside the substation with neutral to operate the disconnect switch and relay. The neural conductor comes out from 25 KV line neutral. My question is there any problem during the fault inside the substation even the GPR is lower than 5000V? The neutral conductor size is #3.Is there any other safety issue regarding this arrangement. I will appreciate for your comments.
Thanks
Bishwajit