Grounding of Switching Station

09/09/2010 2:09 AM

Hi

Can someone give any comments or idea about the grounding issue. I am doing the grounding study for 138 kV switching station. There is no transformer in the station. The calculated ground resistance using CDEGS software is 2.4 ohm. The fault current is 3kA. The measured ground resistance test in the field is 0.82 ohm. To investigate the difference between measured and calculated value, I found that one 120VAC line comes from outside single phase transformer to relay operating panel inside the substation with neutral. That neutral is connected to substation ground grid. The outside single phase transformer connected to 25 kV line and low side 120VAC goes to inside the substation with neutral to operate the disconnect switch and relay. The neural conductor comes out from 25 KV line neutral. My question is there any problem during the fault inside the substation even the GPR is lower than 5000V? The neutral conductor size is #3.Is there any other safety issue regarding this arrangement. I will appreciate for your comments.

Thanks

Bishwajit

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: GROUNDIND OF SWITCHING STATION

09/09/2010 4:16 AM
__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#2

Re: Grounding of Switching Station

09/09/2010 11:20 AM

Did you definitely determine that the lower measured ground resistance vs. the calculated value was due to the bonded neutral? I have often seen CDEGS simulations not match actual measured values due to a variety of reasons, most of which relate to inaccurate soil resistivity data or inadequate modeling of the actual grid conductors in the ground. Also, more often the measured was higher than the calculated.

Having lower actual resistance is good, and the lower the ground potential rise (GPR) the better - it means that when a fault occurs, the current is diffusely distributed in the grid and earth, so that connected equipment does not have as much of an associated potential applied to it (V=IR. Lower R = lower V for the same I). This means lower step and touch potentials, so less danger of shock to personnel and overvoltage damage to sensitive equipment such as relays or communications.

I doubt that you will find much of the fault current will follow the bonded neutral wire. How much a #3 will overheat and whether it will be damaged depends on what percentage of the fault current it carries and how long it takes for your protective relays to trip for the fault and clear it.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Member

Join Date: Aug 2010
Posts: 8
#3
In reply to #2

Re: Grounding of Switching Station

09/13/2010 12:38 AM

Hi

Thanks for your reply. I went to site and found that the neutral coming from 25KV/120VAC transformer(from outside substation) is connected with substation grounding wire. I think it not normal practic. The neutral should not be grounded. The neutral point of pole mounted transformer is grounded which is ok. But the neutral line coming to 138kv switching station with 120vac phase line to operate only the relay for disconnected switch, connected with substation grounding system-is it normal practica? As per CEC code could you do such type of connection? My understanding the metal case of relay panel should be grounded with swithing station grounding system but not neutral conductor.

Register to Reply