DC Fuses Blowing

09/13/2010 10:41 AM

Dear All,

We have the dc common bus feeding the inverters in multidrive application on paper machine. We have faced the serious problem that our dc fuses used to blow on random situations. Sometimes when machine is started and sometimes during running. We have to replace the fuses with the new ones and then machine runs smoothly.Anyone wana give any suggestions to get control of this problem.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: DC Fuses Blowing

09/13/2010 12:44 PM

Yes. Consult an appropriately-qualified local electrician. That individual will have a closer view of the installation and will be able to apply such test equipment as is necessary to form a fair assessment of it and make appropriate recommendations.

After all, the installation cannot be seen from here.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster
#2

Re: DC Fuses Blowing

09/13/2010 4:33 PM

buy big fuses

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3

Re: DC Fuses Blowing

09/13/2010 10:08 PM

DC Semiconductor fuses are special, and faster-acting than normal fuses. It is critical that fuse-selection for this application is done by an expert. Most good fuse companies make such fuses, generally called High-speed semiconductor fuses. Since they have to act very quickly, unless they are correctly chosen, nuisance trip or underprotection will result.

i suggest you ask the fuse manufacturer to recommend the right fuses.

Here is one link :BUSSMANN

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Active Contributor

Join Date: Sep 2010
Location: United Arab Emirates
Posts: 12
Good Answers: 2
#4

Re: DC Fuses Blowing

09/14/2010 12:22 AM

you may need to change the rating of the fuse itself. The fuse rating should exceed the amperage demands of the appliances it protects, so you may have to buy bigger fuses to avoid problems

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#5

Re: DC Fuses Blowing

09/14/2010 2:46 AM

If one associates cost with complexity and technology, and thinks that a fuse is not a technical product, i would recommend downloading and reading this document Bussmann Fuse Training Book

If you use a bigger fuse because the present one is blowing, you are probably losing protection to the drive components. This is not a child's play. It is a serious, professional job of selecting the proper protector for the part to be protected. Otherwise you can as well eliminate the fuses altogether.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Active Contributor

Join Date: Nov 2007
Location: Scotland
Posts: 20
#6

Re: DC Fuses Blowing

09/16/2010 2:31 PM

Without getting too technical, there are occasions, depending on the type of inverter, and the motor it is driving, where, if the drive power is reduced, (say, to allow the motor to slow down), or the DC bus voltage drops, the motor can become a generator for a short space of time, back feeding the DC bus, leading to excess voltages and currents on the DC bus. This is possibly the cause of your problem. I am not an electrical engineer, but have seen big wire wound load resistors, filter networks, and fancy control gear to reduce this excess generated voltage. You need to talk to the manufacturers of the inverters, or an AC drive consultant for a solution to this problem.

Register to Reply