Overload Setting

09/15/2010 1:06 AM

May I know how to set overload setting for motor with DOL starter.

example : motor rated current is 8.80 A. V 415.

2.91 kW. pf 0.85 so I assuming that will be what I need to set overload setting and how I choose to use overload setting . and how to select the mcb also.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Active Contributor

Join Date: Jun 2010
Posts: 15
#1

Re: Overload Setting

09/15/2010 2:11 AM

You can easily select the switch gear and ratings form the catalog of any reputed (ABB, Siemens, L&T) switchgear manufactures. Also these information are available with motor manufactures.

Reply Off Topic (Score 5)
Power-User
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member

Join Date: Feb 2010
Location: dubai,mangalore,bangalore.....
Posts: 145
Good Answers: 8
#2

Re: Overload Setting

09/15/2010 2:29 AM

based on the motor type

olr setting= 115-125% motor flc

mcb = 150-250% motor flc

check out this link

http://cr4.globalspec.com/thread/56416#comment586920

__________________
shamith gambhir, electrical engineer
Reply
Active Contributor

Join Date: Sep 2010
Location: United Arab Emirates
Posts: 12
Good Answers: 2
#3

Re: Overload Setting

09/15/2010 2:39 AM

Its 3 phase so formula is:
I = kW / ( √3 x pf x VLL ), in kA

Reply
Active Contributor

Join Date: Sep 2010
Location: United Arab Emirates
Posts: 12
Good Answers: 2
#4

Re: Overload Setting

09/15/2010 2:40 AM

Run the motor/pump at full load and then tong the cables. then set the starter 10% above that.

Reply
2
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#5

Re: Overload Setting

09/15/2010 3:46 AM

In IEC countries, you need to set the relay at actual motor current, not higher. The relay already has a factor of 1.125 (1.05-1.2 range) built into the trip characteristic as per IEC 60947. If you set the relay higher, it will not protect the motor on overload.

The back up MCB will also need to be set at fairly close to this value. If you can get a 'magnetic-only' MCB, which does not have a thermal element, it will be better. If you want Type 2 co-ordination, it needs more analysis.

As Vinod Tomar says, most good manufacturers give the whole selection. You will be better off using their recommendation.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Overload Setting

08/29/2024 7:10 AM

Assuming the abbreviation <...mcb...> means "miniature circuit breaker", the correct protocol may be found in many countries' electrical standards, such as BS7671 in the UK. Commonly, motor cables are protected by fuses instead.

The relationship between overload setting for the motor and other protection for the cables is called "co-ordination", and forms the training of a qualified Electrician, who is there to design, select, install, test and certify as safe upon completion of the testing. If one is not to hand, then hire someone locally.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Reply to Forum Thread 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

kvsridhar (1); PWSlack (1); SHAMITHGAMBHIR1 (1); Tanuja (2); vinod tomar (1)

Previous in Forum: Sizing MCB   Next in Forum: Fuel consumption per unit

Advertisement