Anonymous Poster

Contactor Coil Burnt

09/15/2010 8:41 AM

Dear Sir

We have one York make chiller at our factory

Starter of this chiller is Star/Delta starter ,we are facing problem of delta coil burnt frequently (Coil volt=110VAC)

Cheked coil voltage found OK

Can you please suggest any remedy to this problem

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: Contactor coil burnt

09/15/2010 9:50 AM

Contactor coil can burnout due to one or more of these reasons:

  • Low or High voltage
  • Full closing of magnet faces prevented by something
  • Shorted turns
  • End-turn insulation failure
  • Impulse voltage
  • High ambient
  • Too frequent starts
  • Control transformer inadequate, resulting in contactor failing to pick up
  • ...

If you give more details of your setup,it will help.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Contactor Coil Burnt

09/15/2010 10:04 AM

Is it open transition or closed transition?

Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: Contactor Coil Burnt

09/15/2010 10:41 AM

Is there a mechanical interlock between the star and delta contactors. Their the favourite for going wrong.

__________________
The reports of my death are greatly exaggerated.
Reply
Anonymous Poster
#4

Re: Contactor Coil Burnt

09/15/2010 11:43 AM

Give more nameplate details perhaps we can fix the problem.

Reply
Power-User
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member

Join Date: Feb 2010
Location: dubai,mangalore,bangalore.....
Posts: 145
Good Answers: 8
#5

Re: Contactor Coil Burnt

09/16/2010 3:05 AM

specify all contactor details, olr, mccb details, motor name plate details.......may be the contactor rating s not proper?

for a little info on star delta starters refer these links

http://cr4.globalspec.com/thread/59853/Star-Delta-Motor-Starters

http://samplecode.rockwellautomation.com/idc/groups/literature/documents/wp/150-wp004_-en-p.pdf

__________________
shamith gambhir, electrical engineer
Reply
Power-User

Join Date: Mar 2010
Posts: 105
#6

Re: Contactor Coil Burnt

09/16/2010 9:52 AM

Dear Sir,

To the comments given by Mr.Sridhar, you can check up the shading

copper ring of the contactor for any breakage or partial obstruction while

closing.

Manroop. Chennai.

Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#7
In reply to #6

Re: Contactor Coil Burnt

09/16/2010 10:33 AM

Ah yes manroop, good point. i missed that, thanks.

However, a broken shading ring would cause a godawful noise, OP you can tell us.

My own vote would be too small a control transformer, since it is 110V. Main and star contactors would pickup together usually, and the inrush current would be too high, voltage would sag, contactors may "pump" (drop off due to low voltage, pickup again with a staccato action), overheat and burn.

Anyway, in the absence of more data, nothing further seems possible.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply