Unbalance in Power System

09/15/2010 2:44 PM

we are having 10/12.5 MVA, 132/11KV, %impedance 8.12%, star/star with nutral ground on both sides. this transformer is loaded with two single phase transformers in addition to three phase transformers, one is connected between R and B phase having 3MVA, 11/3.45KV, %impedance 8.237% No. of phases 01 and another is also connected between R and B phase having 4MVA, 11/3.6KV, %impedance 6.82% No. of phases 01. what may be the unbalance of the system and how to calculate it.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#1

Re: Unbalance in Power System

09/15/2010 4:58 PM

It is not a matter of imbalance or as to how to calculate it, rather the scheme is a conceptual failure.

star- star connection is strictly meant for balanced loads, effect of unbalanced loading is that neutral point shifts resulting in dangerous overvoltages.

Connection of 3+4 MVA transformers on R-B phases, both neutral points grounded,

It is an immidiate distruction !!!

__________________
Knowledge sharing is a WIN-WIN situation
Register to Reply
Anonymous Poster
#2
In reply to #1

Re: Unbalance in Power System

09/16/2010 9:27 AM

But 3MVA 11KV/3.45KV single phase transformer connected between R and B phases is loaded on 10/12.5MVA, 132KV/11KV transformer (which is having tertiary winding in delta connection) from last 10years.