U-value

03/09/2007 4:08 PM

Hello,

I wanted to calculate for the u -value for an insulating material.How do i do the calculation to get the u-value.I need help on this

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Mar 2007
Location: Northeast Pennsylvania, USA
Posts: 173
#1

Re: U-value

03/09/2007 8:18 PM

"R" value is the inverse of "U" value or...."U" value = 1 / "R".

Now.... you CAN'T ADD "R" values! Such as R-13 fibreglass with R-8 iso board doesn't = R-21.

You CAN ADD "U" values though. and then when you're done adding all "U" values, convert to "R".

I suspect "R" value came into being because the average layman and typical consumer/purchaser of insulating materials, could not fathom decimal numbers...

__________________
Unless you're the lead dog on the sled, the view is always the same....
Register to Reply
Power-User

Join Date: Dec 2005
Posts: 125
#2

Re: U-value

03/10/2007 12:21 PM

'u' is a Coefficient of Heat TRansfer and exprerssed in Btu/hr/sf/dtF temp difference. You do NOT add 'u' factors to get total 'u'. But you invert the 'u' factor which becomes Resistance, R, then you add the R's for the various materials you are using; THEN you invert R to obtain total 'u'.

Most often, materials are listed with their 'R' values and is an indication of the insulating quality of the materials. Then, by taking the reciprocal of R you obtain 'u' which is used in the equation

Q(Btu/hr) = (u) x (sf) x(dt)F.

Example: 4" batt fiberglass has an average R value of 11, the 'u' value would be 1/11 or 0.091.

Hope this helps.

Register to Reply
Participant

Join Date: Jan 2007
Location: North Carolina
Posts: 3
#3

Re: U-value

03/12/2007 12:36 PM

There is one more component that must be considered-surface resistance at the air to solid interface also acts to slow the flow of heat. If the surface is the exterior of a building, then wind speed will affect the resistance to heat transfer.

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#4

Re: U-value

03/13/2007 10:03 AM

You don't calculate it. You get the figure from the supplier, and use that to calculate the thickness needed to give the heat flow you want (usually a question of keeping heat flow low). If the results are not to your liking you can then try other suppliers/marerials.

Cheers.....Codey

__________________
Give masochists a fair crack of the whip
Register to Reply