Furnace Power Factor

09/19/2010 1:10 AM

Can I improve the furnace power factor (10 MVA transformer) by installing a capacitor bank after the furnace circuit breaker.incoming is 11 KV

The furnace power factor some time go down up to 0.2 during some case (excessive pressing of electrodes etc) which causes a vibrating sound from secondary side.Does it harm the transformer.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: PF

09/19/2010 2:22 AM

The PF correction needs to be fitted on the furnace side of the transformer. It will take some of the stress off the transformer. The capacitors will have to be switched in and out in banks to correct the PF at the time. I've only worked on induction furnaces but that is where the PF correction was fitted.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User

Join Date: Nov 2009
Posts: 198
Good Answers: 18
#7
In reply to #1

Re: PF

09/20/2010 3:54 AM

Guys this is a strange one, since elements use every watt they get to heat up, and capacitors specifically take care of the "wattless" or reactive currents in appliances, like induction motors where you need excitaion before a rotaing fiels can be setup. How will pf correction improve a furnace efficiency? Or have i misunderstood the post as to the type of elements/probes used, or even the methon of heating used?

I post this "explanation" from somehwere on the web.

Power factor compares the real power (watts) being consumed to the apparent power (Volts-Amps) of the load. A purely resistive load (incandescent lights, electric heating elements.) would have a power factor of 1.0.

__________________
Always learning
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#2

Re: Furnace Power Factor

09/19/2010 10:55 PM

Such a low pf is indeed detrimental. However, you can't have a fixed capacitor all the time since the system pf will go leading when the furnace pf goes higher. You must have a good compensating system with a number of smaller capacitors which can be switched into the system as the pf varies. Induction furnaces always have them. The switching of capacitors is a very severe duty, and is done by special capacitor contactors in LV systems.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Active Contributor

Join Date: Dec 2008
Posts: 19
Good Answers: 1
#3
In reply to #2

Re: Furnace Power Factor

09/19/2010 11:23 PM

I believe, the best technical solution for such a situation is a stepless static compensation which can respond dynamically to the power factor fluctuations and avoid the loss of life of severe switching duty on the contactors and capacitors alike. If the penalties of power factor non-compliance is significant, that can be brought into bounds effectively. It will also address voltage flicker that can have several secondary consequences and provide a healthy power quality in the system.

Disclaimer: We are in the field of providing such solutions. Would be happy to provide more info on it to interested users.

Register to Reply
Associate

Join Date: Sep 2010
Posts: 46
#4
In reply to #2

Re: Furnace Power Factor

09/20/2010 12:40 AM

but I have submerged arc furnace sir where connecting capacitor bank in the secondary is difficult

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6
In reply to #4

Re: Furnace Power Factor

09/20/2010 2:11 AM

It may be difficult but if you want something to ease the stress on the transformer as well as improve general PF, it is where it will have to be fitted.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Associate

Join Date: Sep 2010
Posts: 46
#8
In reply to #6

Re: Furnace Power Factor

09/20/2010 3:58 AM

Running with 0.2 ,0.3 furnace PF with rated current will harm the transformer ?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12
In reply to #8

Re: Furnace Power Factor

09/21/2010 3:32 AM

Not if it has been installed and maintained in accordance with local codes, with all required protective devices under that code in good order.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Nov 2009
Posts: 198
Good Answers: 18
#11
In reply to #6

Re: Furnace Power Factor

09/20/2010 6:02 AM

Apologies, i did not realize that we were talking about an EAF and not induction heaters/elements. however, there seems to be e4nough knowledgable posters on the problem already.

__________________
Always learning
Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#13
In reply to #6

Re: Furnace Power Factor

09/21/2010 4:10 PM

I would be very careful at adding the capacitor on the load side. The transformer is probably acting as a ballast to limit the short circuit current. It acts as a large inductor! The PF compensation is very likely to be done at the primary side.

While the load should provide enough dampening, one has to check for resonances. All the harmonics, sub-harmonics, and in between frequencies will be produced by the arc. The control will need (most likely) to work independently on each single phase.

You need a fast capacitor switch (semiconductors) and controllers for the capacitor banks as the load changes very rapidly (~within 20mS). This is especially true at the beginning of the cycle when the furnace is loaded with coarse material. This period is usually characterized by the electrodes "dancing" up and down.

These people may be able to help you.

http://www.arteche.com/web/frontoffice/Index.aspx?Idioma=2

Good luck.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#14
In reply to #13

Re: Furnace Power Factor

09/21/2010 5:17 PM

Good point. And a GA

My experience is with induction furnaces.

It didn't enter my head about the transformer acting a choke.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Anonymous Poster
#5

Re: Furnace Power Factor

09/20/2010 1:00 AM

Please approach Siemens for solution

Register to Reply
Active Contributor

Join Date: Mar 2009
Location: Makassar, Central Indonesia
Posts: 15
#9

Re: Furnace Power Factor

09/20/2010 4:05 AM

Can you check what is the average time of a certain PF value ? If it is long enough, than you can put step PF at the secondary side of the transformer.One thing you have to remember that your process is the same as short circuiting the transformer secondary dide, that's why the transformer vibrates. I have the same experience with such steel arc furnace, we use a 5 MVA transformer 70 kv / 20 kV, to supply the arc furnace transformer, this transformer has been designed to be able to withstand the short circuit current shock. So I believe that your arc furnace transformer should be able to handle it too.

Of course using Static VAR Compensator is the best way, but as I know it's very expensive. please try with conventional step capacitor but with oversized contactor.

regards,

Stanyadji

Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#15
In reply to #9

Re: Furnace Power Factor

09/23/2010 3:51 PM

I would be surprised if you had a capacitor bank at the secondary of your transformer. Can you confirm?

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Active Contributor

Join Date: Mar 2009
Location: Makassar, Central Indonesia
Posts: 15
#16
In reply to #15

Re: Furnace Power Factor

09/23/2010 11:37 PM

Dear Marcot,

Yes we have the capacitor in the secondary side of the 70 kV/ 20 kV transformer, but the furnace has its own step down transformer. Our transformer is the public Utility transformer which supply the steel factory. I believe it's a misunderstanding, the capacitor isn't connect to the furnace transformer secondary side.

regrds

Register to Reply
Member

Join Date: May 2010
Location: Kampala, Uganda
Posts: 7
Good Answers: 1
#10

Re: Furnace Power Factor

09/20/2010 5:05 AM

Whatever the solution you will finally arrive at, you also need to take into consideration any harmonics that can be generated by the furnace and injected into your power distribution network.

Furnces are among the leading generators of harmonics in power distribution networks. Therefore, you will need to install harmonics filters along with any power factor correction capacitors. If you do not install the filters, then your capacitors may blow within a few hours of operation. Morever these harmonics could also cause havoc in other equipment within you power distribution network (if you have not yet experineced it already, that is)

The professional approach I would recommend is that you first carry out a power line analysis including for harmonics (this may require a consultant). The results of the analysis will give a clear picture of trends of voltage, power consumption, power factor and harmonics (you may need to specify what you need in terms of reference for the analysis). Any power factor correction equipment manufacturer can use the power line anlysis results to design the suitable filters for your capacitors. You will also need to specify what value you need to bring your power factor to so as to determine the KVAr capacity for the capacitors you need.

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#17

Re: Furnace Power Factor

10/04/2010 11:44 AM

Contact the furnace manufacturer

__________________
pnaban
Register to Reply
Register to Reply 17 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!