Parallel Circuit Breakers

09/19/2010 3:12 AM

can we parallel two circuit breakers to make a bigger one for example can we parallel two cb with a and b rating to make a+b?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: parallel circuit breakers

09/19/2010 4:02 AM

Sure

Then set up a hot dog stand to sell refreshments to the people watching the flames

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: parallel circuit breakers

09/19/2010 4:53 AM

What voltage and rating are the breakers? It can be done but only with the correct protection.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#3

Re: parallel circuit breakers

09/19/2010 9:38 AM

No, you can not do it by yourself, but it is allowed to be assembled in factory where the system undergoes all sort of testing . Here is the quote from the NEC regarding the use of fuses or Circuit Breakers in parallel:

"240.8 Fuses or Circuit Breakers in Parallel. Fuses and circuit breakers shall be permitted to be connected in parallel where they are factory assembled in parallel and listed as a unit. Individual fuses, circuit breakers, or combinations thereof shall not otherwise be connected in parallel."

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#4

Re: Parallel Circuit Breakers

09/19/2010 2:51 PM

Short answer no, long answer - almost always no. There are some cases where parallel circuit breakers can be used when linking different sources together, but NEVER two circuit breakers in parallel on the same source!

The same goes for fuses if you were wondering.

__________________
jack of all trades
Register to Reply
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#5

Re: Parallel Circuit Breakers

09/19/2010 5:23 PM

I have a photo that I wanted to post,but can't find it at the moment. It shows a 3P 63A MCB with all 3 poles commoned together at each end, functioning as the protection device for a DC power system.

If I hadn't seen it done, I would have said NO , you can't do that. Actually, at the time I did say NO, and the DC power systems engineer that I was discussing this with said 'You may not be allowed to do this in an AC system, but we do it all the time to protect DC power systems'.

__________________
paulusgnome
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6
In reply to #5

Re: Parallel Circuit Breakers

09/19/2010 9:17 PM

Just because you CAN doesn't mean you SHOULD.

If you do that with lets say a 30A 3P breaker, the sensing elements are still 30A. As soon as ANY ONE pole hits 30A it would trip. So you did not really make a 90A breaker, you made a 30A breaker with redundant power paths.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#7

Re: Parallel Circuit Breakers

09/20/2010 1:56 AM

In mathemetics 2 plus 2 makes four but not in the electrical world.

Any two CB's, no matter from the same manufacturer of same or dfferent ratings have fractionally different time of operation, fault sensors inbuilt have difference in magnitude of trigger sensing and upto 15% is standard deviation.

Take into account short circuit tripping, the comparatively long time delay in circuit opening by one of the two will cause symmetric faults to be unsymmetric, duration of first current peak will be prolonged causing the system to yield, the time deviation will also cause travelling surges of unusual proportion for the whole system protections to be in jeoperdy.

To fulfill your ambition I suggest you join a manufacturer whereby at the test bench you can pluck 2 components from a whole lot to be of coincidal symmetrical characterstics to work in parallel.

__________________
Knowledge sharing is a WIN-WIN situation
Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); jack of all trades (1); JRaef (1); mountk2 (1); msamad (1); Paulusgnome (1); TonyS (1)