Comparison Between LT VVFD VS MV Soft Starter

09/19/2010 6:06 AM

For 2.2KM lengthy conveyor we have planned to install 2 x 250kw 6.6KV motor now we are thinking of changing over to LT VVFD or 6.6KV soft starter can any body suggest which one is better the intention is smooth starting of the conveyor.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor

Join Date: Sep 2008
Posts: 20
#1

Re: Comparison Between LT VVFD VS MV Soft Starter

09/19/2010 11:09 PM

I am not trying to answer this question and I understand you already have the conveyor in place. But I thought you may be interested in this new invention. A conveyor with multiple drives along the belt. http://www.innovativeconveying.com

__________________
"A designer knows he has achieved perfection not when there is nothing left to add, but when there is nothing left to take away."
Register to Reply Off Topic (Score 5)
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Comparison Between LT VVFD VS MV Soft Starter

09/20/2010 12:17 AM

Best is a subjective term. VFDs for 2 x 250kW motor in low voltage will probably be more expensive than a single 6.6kV soft starter running two motors, so from an initial cost standpoint, the SS would be best. Smoothest start? VFD without question. A VFD can accelerate the conveyor at any speed stretched out over any amount of time. But having two VFDs allows you the flexibility to ensure that the motors are equally sharing the load, soft starters cannot do that. A 2.2kM conveyor belt will act like a rubber band then accelerating, so VFDs allow compensation where soft starters cannot. VFDs can also allow for some breaking capacity if any part of the conveyor goes down hill.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Associate

Join Date: Jun 2010
Location: INDIA
Posts: 27
Good Answers: 1
#3

Re: Comparison Between LT VVFD VS MV Soft Starter

09/20/2010 2:20 AM

GO FOR

6.6kV RANGE 250MW VFD EITHER WITH VECTOR CONTROL OR DTC CONTROL FROM REPUTED MAKES EITHER ALLEN BRADLEY OR ABB.

PREFERABLY INDEPENDENT DRIVES FOR BETTER CONTROL AND CONDITION MONITORING/RELIABILITY.

__________________
S BHATTACHARYA
Register to Reply
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member Popular Science - Genetics - New Member Technical Fields - Technical Writing - New Member Safety - ESD - New Member Engineering Fields - Power Engineering - New Member

Join Date: Jul 2010
Location: INDIA MUMBAI
Posts: 67
#4
In reply to #3

Re: Comparison Between LT VVFD VS MV Soft Starter

09/20/2010 2:50 AM

6.6kV VFD are very expensive

__________________
Correct Me If Iam Wrong, Suggestions/Recommendations needs to be verified before implementation
Register to Reply
Register to Reply 4 comments
Copy to Clipboard

Users who posted comments:

bsekhar (1); cool (1); JRaef (1); sms149 (1)

Previous in Forum: Parallel Circuit Breakers   Next in Forum: Deatail of Setting in 7SJ600
You might be interested in: Conveyor Controls and Monitors, Conveyor Rollers

Advertisement