Soft Starter

09/21/2010 9:51 PM

How does a soft starter work in a D.O.L.starter panel?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Soft Starter

09/22/2010 12:11 AM

DOL circuit output is given to soft starter.which inturn speed up the motor smoothly. DOL just acts as a switch for the soft starter.

Reply
Member

Join Date: Jun 2010
Posts: 7
#2

Re: Soft Starter

09/22/2010 12:54 AM

A soft starter just like a VSD ramps a motor up to feed using power factor and frequency till full load RPM is reached

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Soft Starter

09/22/2010 4:04 AM

Is the Wikipedia article on soft starters not available in that part of the world?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Soft Starter

09/22/2010 12:30 PM

I think for the most part a Soft Starter is used INSTEAD of a DOL starter. If you put a DOL starter in from of a Soft Starter, it becomes simply an Isloation Contactor, so it is no longer a "DOL" starter. If you put it in parallel to the Soft Starter, it becomes a Bypass Starter.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Score 1 for Good Answer
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#5
In reply to #4

Re: Soft Starter

09/22/2010 8:06 PM

Softstarters can be used in different fashions such as (1) In-Line and (2) Internally bypassed and (3) Externally bypassed.

(1) In-Line: The softstarter always remains in line and motor receives power from the thyristors all the times. This allows the motor to stop with the softstarter but there is a power loss keeps occurring in the thyristors and additional cooling system is required for large size softstarters.

(2) Internally bypassed: In this case, the softstarter itself contains the in-built bypass contactor which is also a part of the softstarter. After the motor start is over, the thyristors of the soft starter are bypassed with the contactor. This minimizes the power loss within the thyristors during the motor running condition.

(3) Externally bypassed: Softstarter is connected in parallel to the DOL starters. Once the motor starting is complete, the softstarter is bypassed with the motor starters and it is completely isolated from the system. The starter takes care of the motor protection system during the motor running condition. A single softstarter may be used to start multiple motors in this configuration. It doesn't allow the motor for soft stopping.

It seems to me the OP's question is related to the configuration 3.

This link may help:

https://www05.abb.com/global/scot/scot209.nsf/veritydisplay/2985284834bcff7fc1256f3a00274038/$File/1SFC132002M0201.pdf (page 64)

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply
Reply to Forum Thread 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); JRaef (1); msamad (1); PWSlack (1); ronaldnaidoo (1)