Delta Motor Taking More Current

09/22/2010 11:31 PM

Dear All

One of our new motor ( 3.7 KW, 415 V,FLA 6.6 A, 50 HZ Delta connected, Efficiency : 86%) during the no load trail run it has taking more staring current(around 70 A)

and running current 15 A then tripped. After that, we changed the connection from Delta to Star. In star position it is taking starting current is 42 A, and running current is 5.5 A

Anybody can explain what the reasons for happening like this are.

with rgards

JCG

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: Delta connected motor taking more current

09/22/2010 11:59 PM

If started DOL in delta, the motor can take 6-10 times the rated current during starting, 70A seems just about ok, though rather high. Running current of 15A is not ok at all. All three lines take 15A? Or only one ? If one, then some short in one winding.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Active Contributor

Join Date: Feb 2010
Posts: 24
#2
In reply to #1

Re: Delta connected motor taking more current

09/23/2010 1:24 AM

Dear sir

Motor staring with DOL only and all three phase is taking almost is same current 15 A.

with regards

JCG

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3
In reply to #2

Re: Delta connected motor taking more current

09/23/2010 1:32 AM

Then this is rather strange. It is behaving like a 7.5 kW motor. i am sure you would have checked with the motor manufacturer, what does he say? If the motor was to be run as a star-connected one, the star point would have been made inside and you would have access to only three leads, so it seems to be meant to run in delta mode.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Active Contributor

Join Date: Feb 2010
Posts: 24
#4
In reply to #3

Re: Delta connected motor taking more current

09/23/2010 1:52 AM

This motor make by ABB Type EHX132SMB2 (6 lead out) and supplied through our contractor they are communicating with with ABB and we are waiting for their reply.

Thanks

JCG

Register to Reply
Member

Join Date: Jul 2010
Location: CHIPLUN, Maharashtra
Posts: 8
#7
In reply to #4

Re: Delta connected motor taking more current

09/24/2010 12:18 AM

Does the motor new or rewinded? If rewinded then there may be defect in rewinding.

Register to Reply
Active Contributor

Join Date: Feb 2010
Posts: 24
#8
In reply to #7

Re: Delta connected motor taking more current

09/24/2010 1:49 AM

Its new motor

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#9
In reply to #8

Re: Delta connected motor taking more current

09/24/2010 2:02 AM

Most likely #5 by JRaef is right. The current when star-connected seems to be the rated one. You can also see if you have 3φ 240V and check the motor in Delta.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5

Re: Delta connected motor taking more current

09/23/2010 2:24 AM

6 lead motor is most likely designed to connect in a Delta pattern for low voltage, 240V, and a Star pattern for High voltage, i.e. 415V. If you put 415V on the motor when connected in Delta, you would be over saturating it and the current would be high without producing more torque.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6

Re: Delta connected motor taking more current

09/23/2010 4:43 AM

It sounds it could be phase reversal

IE

A1 > A2

B2 > B1

C1 > C2

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#10

Re: Delta Motor Taking More Current

09/24/2010 8:19 AM

In addition to the all points as already stated, please also check the airgap between rotor and stator and condition of bearings i.e. whether there is any jamming or defects in bearings.

__________________
Manindra
Register to Reply
Associate

Join Date: Aug 2010
Location: UAE
Posts: 50
#11

Re: Delta Motor Taking More Current

09/24/2010 8:33 AM

check the nameplate or cover of motor. you will see delta - y connection for 230v and 380v. this means your motor can run on either supply and mostly delta for 230v 3phase supply and 380v 3phase for y.

Register to Reply
Active Contributor

Join Date: Feb 2010
Posts: 24
#13
In reply to #11

Re: Delta Motor Taking More Current

09/24/2010 11:25 PM

Dear Sir

The motor nameplate details are as given below

Make : ABB

Type : EHX132SMB2

Duty : S1

Sl. No : 436501

KW /HP : 3.7/5.5

Speed : 2915 RPM

Voltage : 415V

Frequency : 50Hz

Current : 6.5A

Power factor : -

Efficiency : 86%

Connection : DELTA.

Bearing DE : 6308ZZC3

Bearing NDE : 6307ZZC3

Winding Resistance Test: (Values in Ohms) (Using Equipment Details)

Equipment: Multimeter : Make: fluke Range: 0-1000v

RefValues
U1-U26.2
V1-V26.2
W1-W26.2

Regads

JCG

Register to Reply
Associate

Join Date: Aug 2010
Location: UAE
Posts: 50
#16
In reply to #13

Re: Delta Motor Taking More Current

09/25/2010 3:14 PM

mostly motor of 380v and above are on y connection. maybe you are confuse of d in the nameplate. please check the cover of motor connection usually the right connection is inscribe inside of the cover. for a high starting load since this a small motor take some further examination. open it and check the bearing and insulation. if found okay. check the contactor (contact point) that supply the power.

lastly refer to manufacturer.

Register to Reply
Active Contributor

Join Date: Feb 2010
Posts: 24
#14
In reply to #11

Re: Delta Motor Taking More Current

09/24/2010 11:35 PM

Dear sir

In star position motor running smoothly, (running current is 5.5 A) that means no more jamming

Regards

JCG

Register to Reply
Associate

Join Date: Aug 2010
Location: UAE
Posts: 50
#12

Re: Delta Motor Taking More Current

09/24/2010 8:43 AM

kindly send all the information you see in the nameplate.

Register to Reply
Power-User

Join Date: Oct 2007
Location: Canning Vale Western Australia.
Posts: 160
Good Answers: 7
#15

Re: Delta Motor Taking More Current

09/25/2010 4:17 AM

Take a good look at the name plate. You will most likely find that it is 415V star connected and 240V delta connected. A lot of the cheaper motors are comming out this way, the electricians at our plant have been caught several times with this.

__________________
I attend work so my dogs can have the good life.
Register to Reply
Member

Join Date: Jul 2010
Location: CHIPLUN, Maharashtra
Posts: 8
#17

Re: Delta Motor Taking More Current

09/26/2010 12:07 AM

In star connection couple the motor with load & check motor current & temperature rise, if found abnormal it showes defective winding, OR check by rewinder.

Register to Reply
Register to Reply 17 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Doggoneit (1); erlo (3); jcg154 (5); JRaef (1); kvsridhar (3); manindra (1); TonyS (1); VIJAYANAND (2)