Previous in Forum: AH of Battery   Next in Forum: 3 Phase Transformer
India - Member - PROFESSIONAL Engineering Fields - Power Engineering - electrical planning - designing
Voltage Level
09/23/2010 3:08 AM
dear all,
kindly get me reply with reference"-
classification of voltages per GERC are as < 440 low voltage
IEC are as < 1000 volts.
While the VVFD at 690 V, treated by Electrical inspector as HT , which i do not agree, since the supply code defines for supply of power . 100 kw at 11 kv, while we do operate even higher kw motor say 250 kw with soft starter or vvvf etc.
Regards
Good Answers: 181
Re: voltage level
09/23/2010 3:34 AM
CR4 Admin: Deleted Post
Abuse/Attack: This post was deleted because it was an attack on another user. Please review the CR4 Site FAQ and the CR4 Rules of Conduct.
Good Answers: 170
Re: Voltage Level
09/25/2010 11:48 PM
Classification of Voltage Levels – Indian & International Practices
by: K.Sivakumar, Manager – Training, Switchgear Training Centre, Larsen & Toubro Limited, Coonoor, T.N.
Synopsis: As electrical professionals, many of us have been coming across the terms LV or LT, MV, HV or HT & EHV or EHT in our day-to-day professional lives. But, are we aware of the limits of these voltages as per Indian Standards and/or International Standards? This article aims to anlayse the limits set for these voltages in Indian as well as International Standards.
Foreword: Voltage levels have been defined and classified by various National and International Standards as also by certain electric power utility companies. The following are the definitions given in various Indian & International Standards for AC Voltages.
India: As per the Indian Electricity Rules, 1956, vide Rule 2(av), the following are the limits:
Low Voltage: Not exceeding 250V
Medium Voltage: Not exceeding 650V
High Voltage: Not exceeding 33000V
Extra High Voltage: Exceeding 33000V
But, in IS 13234 – 1992, which is the "Guide for short-circuit current calculation in Three-phase A.C. Systems" – it is mentioned vide Table I that:
Low Voltage: 100V to 1000V
Medium Voltage: > 1kV to 35kV
High Voltage: > 35kV to 230kV
As can be seen from the above, there is no harmony between the IS and the IE Rules in this issue.
France: Vide a publication dated 14th November 1998, the French Regulations define three voltage levels as below:
Low Voltage: < 1kV
High Voltage A (HTA): > 1kV but </= 50kV
High Voltage B (HTB): > 50kV
CENELEC (The European Electrotechnical Standardisation Committee): Vide a publication dated 27th July 1992, the CENELEC recognises the following voltage levels:
Low Voltage: < 1kV
Medium Voltage: > 1kV but </= 35kV
IEC (International Electrotechnical Commission): In IEC 60071, the following ranges are defined:
Low Voltage: < 1kV
High Voltage Range I: > 1kV but </= 245kV
High Voltage Range II: > 245kV
The acronyms EHV (Extra High Voltage) and UHV (Ultra High Voltage), though are being used elaborately in India, have never been officially defined in any of the above three standards.
USA:
i) Vide IEEE Std. 241-1990 (IEEE Recommended Practice for Electric Power Systems in Commercial Buildings), Clause 3.1.1.2,
Low Voltage: A class of nominal system voltages 1000V or less
Medium Voltage: A class of nominal system voltages greater than 1000V and less than 100000V
High Voltage: A class of nominal system voltages equal to or greater than 100000V or less than 230000V
ii) Vide ANSI C84.1-1989 (Voltage ratings for electric power systems and equipment),
Low Voltage: 120V to 600V
Medium Voltage: 2400V to 69000V
High Voltage: 115000V to 230000V
iii) Vide ANSI C92.2-1987 (Power Systems – Alternating Current Electrical Systems and Equipment Operating at Voltages above 230kV Nominal – Preferred Voltage Ratings)
Extra High Voltage: 345000V to 785000V
Ultra High Voltage: 1100000V
Note: IEEE – Institution of Electrical and Electronic Engineers
ANSI – American National Standards Institute
Conclusion: As can be seen from the above, there is no clear cut demarcation for classification of various voltage levels in AC Electric Power Transmission and Distribution. Also, there is no single standard across the globe, with various countries defining various limits for these voltages. And, as in the case of India and USA, even within one country, two standards do not match, when it comes to these limitations. It is wished that the electrical community across the globe meets and takes a decision soon to bring harmony across the countries of the world in standardizing the limits for various voltage classifications.
Re: Voltage Level
10/01/2010 5:24 AM
IS 12729 :204 Common specifications for high voltage switch gears and control gears STandard , 1.1 scope : This standard applies to a.c. switchgears and controlgears , designed for indoor and outdoor installation and for operation at service frequnecies up to and including 50 HZ on system having voltage above 1000v.
Does this means voltage below 1000v are not HT Voltage? as stated in IE Rules and CERC
IS 12360 Voltge Bands for Electrical Installations including preferred voltage and frequency
The standard cl 0.7 states as 1000volts forms boundry between low voltage and high voltage
Register to Reply 3 comments
electricalexpert65 (1); nascon (1); TonyS (1)