siemens micromaster 430

09/24/2010 10:32 PM

Hi guys,

just got a new vfd siemens vfd micromaster 430, intended for air compressor motor. motor datas: vfd ready siemens motor, 400vac, 3phase, 50kw, 4000rpm, 120amps, 160hz at full rpm. vfd is 55kw, 3 phase. i got to control the speed by way of analog input (pressure). at 900rpm, the compressor will start to load by way of relay output. set pressure is 90psig max, when at this steady state pressure for about 2 minutes, the compressure will shut down. the configuration manual provided do not include PID configuation and such other extended configuration, except only the basic or standard configuration. can anyone help me please?

Thanks and much appreciated

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Member

Join Date: Jul 2010
Posts: 7
#1

Re: siemens micromaster 430

09/26/2010 11:32 AM

I think this is nothing to do with VFD setting. Air compressor usually come with pressure switch to shut down the compressor once the max pressure reached.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#2

Re: siemens micromaster 430

09/26/2010 2:25 PM

If I guest you right, You have a screw compressor (maybe ATLAS COPCO...) with VFD siemens Micromaster 430.

You want to use this directly without the dedicated PLC controller supplied with the compressor ?

I can only give some hints on the way to control the Inverter with the PID but you need to do most of the parameters settings yourself. Always try the settings with the motor uncoupled from the compressor and do some simulation on the feedback to verify it is working the way you want:

- PID feedback input must be from a pressure transducer giving the required 0 to 10V signal to cover the range of pressure you want. Select the PID feedback location parameter P2264 to be 755.01 which means that you will use the Analog Input 2 for this feedback.

- PID Set point input should be also an analog signal entering Analog input1, and also varies from 0 to 10V.

This setpoint signal must be rigged so that you can set the pressure required by varying the signal value. (Potentiometer can be used...).

The PID will compare the 2 input signals and will increase/decrease the motor frequency to increase/decrease the rpm and attain the required pressure and maintain it.

the minimum and maximum rpm are set somwhere else.

All the PID controller parameters should be looked at and understood to set them properly for the operation to be correct. Do tests without driving the compressor element but only the motor. Rig the feedback to simulate pressure values and see if you have selected the parameters correctly.

I hope that you only needed the above info Otherwise i cannot pretend to configure it completely for you. This would require more checks and some experience in using the same installation whish I do not have now.

The OEM PLC does the PID Job externally and controls the frequency of the inverter directly.

Register to Reply Score 1 for Good Answer
Commentator

Join Date: Jul 2010
Posts: 75
#3
In reply to #2

Re: siemens micromaster 430

09/26/2010 8:00 PM

Hi Lucke,

thank you so much for the help. this is my first time to configure the siemens vfd. furthermore, as i have read on the manual, on the application macro, MM430 is only applicable for pumps and fans, just want to be clarified if these MM430 is also applicable for air compressor?

once again, thank you so much

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#4
In reply to #3

Re: siemens micromaster 430

09/27/2010 6:42 AM

For Piston Compressors, you need to make sure that the VFD can be set to constant torque in the first place. Also, there will be a minimum rpm for this type of compressors not to go below otherwise you will compromise the efficiency and affect the smoothness of the running... But for the screw types and centrifugal compressors, it will be easier to work with. Atlas-copco uses the MM440 series.

Register to Reply Score 1 for Good Answer
Commentator

Join Date: Jul 2010
Posts: 75
#5
In reply to #4

Re: siemens micromaster 430

09/27/2010 7:19 PM

thanks for the assistance. i can now have the option.

much appreciated

Register to Reply Score 1 for Good Answer
Register to Reply 5 comments