Excess Air and CO

09/30/2010 11:48 PM

I have some questions about typical range/ovens burners. Maby there one or two "hoofs" out there that can answer these. What is the percentage excess air (optimum) in the oven burner using nat gas at sea level, then what is it at 8,000' same gas? Will changing this percentage decrease C O. Does the hood spud need to be changed (de-rated) to a smaller size? Last but not least, why do the manufactures and their installers allow so much C O to come from their gas ranges at altitude?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Commentator

Join Date: Jan 2006
Location: Western flank of the Pennines in Lancashire England
Posts: 93
Good Answers: 8
#1

Re: Excess Air and CO

10/02/2010 3:27 AM

I am not sure what a "hoof" is but I will try and address your questions.

Firstly the optimum excess air required by any burner is a function of the fuel to be used,the burner design and the aerodynamics of the combustion chamber, oven space and load and finally the flue. The maximum permitted CO concentration will depend on local code but in practice should not exceed 100ppm (parts per million of the flue gas) regardless of the altitude at which the appliance is operating. In the absence of local code I have just measured the flue gases exiting the flue of my light commercial range at home and got the following results on both ovens running on propane:

Altitude - 1050ft

CO - 50ppm

Co2 - 9.4%

Excess air - 46%

Flue exit temp 449oF

The values above are entirely in line with what I would have expected whether using NG or propane.

then what is it at 8,000' same gas?

This is where the aerodynamics of the appliance comes in. As the density of the air at 8000' will be less than at sea level, the flame envelope will increase in size and may impinge of parts of the oven that it did not reach at sea level where it was probably tested. Flame impingement is a known cause of high CO levels. As we don't have any NG appliances at 8000' here in the UK I cannot give you a definitive value for the end result. However the commissioning engineer should have checked the level of CO and made any adjustments necessary.

Does the hood spud need to be changed (de-rated) to a smaller size?

This would be one possible way of reducing an excess level of CO. A smaller jet running at a higher pressure to maintain the heat input, would create a tighter flame with more air mixed in it, reducing the flame envelope back to the sea level size eliminating flame impingement.

why do the manufactures and their installers allow so much C O to come from their gas ranges at altitude?

As you have not specified the amount of CO being produced it is difficult to answer this question. In defence of the appliance manufacturer appliance design is not the only cause of CO production. If the kitchen is not adequately ventilated CO will be produced. I guess that at 8000' it gets cold and you may have limited ventilation to keep warm. Is there an extract system in operation above the appliance? Is it interlocked with the gas supply so that the extract has to be running before the appliances can be used? Is there sufficient air inlets in the kitchen to replace the air being extracted by the canopy?

Regards,

Gasman

Reply Good Answer (Score 2)
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#2
In reply to #1

Re: Excess Air and CO

10/02/2010 9:51 AM

GA

I would add that if the CO is high when you have excess air in the range of 10% and above, it will be an indication of bad air mixing and bad combustion environment: If the velocity of the air flow is too high, it will entrain the combustion mix too fast out of the flame zone and thru the chimney. The flame shape and the optimum air volume/speed is important for a complete combustion and low CO in the exhaust gases.

I have more experience in Fuel Oil furnaces rather than Gas. Does it apply to the Gas fired furnace?

Reply
Commentator

Join Date: Jan 2006
Location: Western flank of the Pennines in Lancashire England
Posts: 93
Good Answers: 8
#4
In reply to #2

Re: Excess Air and CO

10/03/2010 5:03 PM

Yes. When firing a forced draft burner with any fuel gas and there is too much air going in through the burner or the air flow over the root of the flame is too fast the combustion process can be stopped before completion. The result is the presence of a group of chemicals in the exhaust gases called Aldehydes. The most well known one is Formaldehyde and this is known to irritate the mucus membranes (eyes & nose) making them run and itch. Mot flue gas analysers will show this as CO which is really un-burned hydrocarbons. So increasing the air supply too burners like this can make the problem worse. It does not apply as much to atmospheric injected burners as commonly fitted to catering equipment. These rely on the kinetic energy in the gas to induce some of the air required for complete combustion and are normally designed to produce a mixture in the burner containing about 60% of the total air required. The rest is introduced into the combustion chamber as secondary air.

Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#5
In reply to #4

Re: Excess Air and CO

10/03/2010 7:44 PM

Thanks for the reply Gasman.

Reply
Anonymous Poster
#3
In reply to #1

Re: Excess Air and CO

10/02/2010 11:03 AM

Thanks for your reply. A hoof is a" Hands On Old Fart ". And i mean old. The oven in question was putting out 900 PPM CO, and I think that the manufactures know this, but say nothing. The manufactures have their burners tested by company's like Gas Consultants Inc. And from what I can see they have it down pat. They use very precise math. A good running oven should only about 7 PPM CO. ovens continue to put out massive amounts of CO. because the installation Manuel says only to crank down the hood orifice with a 1/2" wrench, and change the regulator. This converts the burners to sea level LP only, and ranges are not adjusted and tested when installed at altitude. The service Manuel's should be changed to reflect this.

Reply
Commentator

Join Date: Jan 2006
Location: Western flank of the Pennines in Lancashire England
Posts: 93
Good Answers: 8
#6
In reply to #3

Re: Excess Air and CO

10/04/2010 7:44 AM

It sounds like your installer/commissioning engineer is not up to the job. He should hve spotted the high CO and done something about it. That is after all what you paid him for.

Reply
Power-User

Join Date: Mar 2010
Location: The Canyons of the Ancients
Posts: 356
Good Answers: 2
#7
In reply to #6

Re: Excess Air and CO

10/08/2010 10:48 AM

who tests the oven in your kitchen with a combustion analyzer? if you find one, have them get in touch with me. and it is one thing to test and another to fix the problem. (too much CO from ovens is a big unnoticed problem) ALWAYS WELL VENTILATE YOUR KITCHEN.

__________________
" looking for conscience in the brain is like looking for the band in the radio" N. H.
Reply
Commentator

Join Date: Jan 2006
Location: Western flank of the Pennines in Lancashire England
Posts: 93
Good Answers: 8
#8
In reply to #7

Re: Excess Air and CO

10/08/2010 1:41 PM

We do not have a problem in the UK with height affecting the combustion of commercial kitchen equipment as the max elevation here is not great enough but I know it is a problem in the USA as this sort of question has been asked in previous postings.

As part of the UK system of proving competence anyone installing gas fired equipment needs a flue gas analyzer and the appropriate proof of competence before he is let loose on the public. Give the way professional competence is regarded in the USA I am surprised that a gas engineer over there is not required to test for CO when installing a range or oven at 8,000'. The ultimate solution is in the hands of the appliance designers and the test houses used. I was going to say that combustion engineering is not rocket science but it is. As a student gas engineer I had to study jet propulsion as well as gas burner design.

To reinforce you shout at the end:- in the UK a commercial kitchen is required to have an exhaust system and its associated fresh air inlet interlocked with the gas gas supply in such a way that the gas supply is interrupted unless the canopy fan is running correctly. The gas supply is only restored when all the gas taps have been proved to be closed by an automated gas tightness test using a pressure switch and a calibrated jet in a bypass around the main safety shut-off valve.

Reply
Reply to Forum Thread 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Gasman (4); LAA_Lucke (2); munch (1)

Previous in Forum: How to Season a Green Birch Stump   Next in Forum: Quick Fix Adhesive How to Remove Strains
You might be interested in: Burners, Laboratory Ovens, Vacuum Ovens

Advertisement