10/02/2010 9:17 AM
HOW CAN WE CALCULATE THE EXHAUST FLUE PIPE/DUCT?
We have 3 MW X 3 Diesel Gensets , the Exhaust from each Diesel Genset(DG) is 19,492 kg/hr (23410 cu.ft/min) @ 450 DEG C , So from three DGS = 3*19492 KG/HR = 58476 KG/HR ( 3* 38984 = 116,952 cu.ft/min), This amount of Exhaust flue gas is passed thru ABSORPTION CHILLER FOR HEAT RECOVERY & the temp after passing thru chiller drops down from 450 to 160 deg C , With this 160 DEG Temp at the outlet of ABSORPTION CHILLERS , the weight FOR EXHAUST GAS being the same the mass flow rate @ 160DEG C becomes , 3*19492 KG/HR = 58476 KG/HR ( 3* 26129 = 78,387 cu.ft/min). I want to size the exhaust flue pipe/duct.
Can some body guide me how to do that , from where shall i get the material to refer.
I appreciate for any of the input.
Thank you very much
Mirza
Re: Exhaust Flue Pipe/Duct Sizing
10/02/2010 10:11 AM
There are many ways to find the answer online, piping calculators. If you want to know how concept, i guess you would need to steal the fluid book somewhere. I hope this help
-R
Good Answers: 137
10/02/2010 4:30 PM
Comparing the engine exhaust pipe diameter and the chiller intake gives you a starting point. If it were just 1 engine, 1 chiller I'd use the bigger of the 2. If it's 3 engines feeding 1 chiller, it's slightly more complcated, but you can still compare pipe areas.
Cheers............Codey
Good Answers: 19
10/02/2010 6:39 PM
Mr.Mirza, the Chiller Manufacturer gives his drawings which not only indicates sizes/dimensions but also location of diverting motorized valves and P & I Drawings of complete system. Suggest you get these from your Chiller suppliers.Any excess pressure drop due wrong sizing , both the generator & chiller manufacturers will put blame on you.Suggest you call engineers from both suppliers to discuss this.
10/03/2010 9:52 AM
You have to follow Mr. Ducon's suggestion. However to understand the theory of duct design you can refer any air conditioning text books .
10/03/2010 12:38 PM
Good morning Guest. If each DGS emits 23,410 cfm, the total for all 3 would be 70,230 cfm, not 116,952 cfm.
10/04/2010 4:04 AM
Actually that is 38984cfm mass flow @ density of 0.5 kg/m3 at 450 deg C at the outlet of DG for 19492 kg/hr weight, so for 3 DGS 3*38984 = 116952 CFM 7 NOT 70230 CFM. The 23,410 cfm is typo error.Thanks for that.
10/04/2010 8:16 AM
I have wanted to do things like this but never had the money.
One consideration I have always thought prudent would be to monitor the exhaust gas back-pressure as changes are made.
By using inducer fans and pressurizing the exhaust, or exhaust fans and creating a negative pressure, I would think it wise to maintain the same back-pressure as the manufacturer sent the machine out the door with.
Who is so ignorant as not to know that knights-errant are beyond all jurisdiction, their only law their swords, while their charter is their mettle and their will is their decrees? Don Quixote
Good Answers: 19
10/04/2010 8:43 AM
Coldspot you are scareing Mirza