Previous in Forum: PLC contact for motors   Next in Forum: How to Use DP Transmitter for Fressure, Flow, Level
Differential Flow Meters Calculation in Squre Root
10/02/2010 1:14 PM
How to calculate squre in a differential flow meters
Re: Differential Flow Meters Calculation in Squre Root
10/02/2010 9:37 PM
Dear
If you mean flow rate calculation:
liquid flow is Qe =(Q).(Gl).sq of 1/Gf
Qe(flow rate).Q(upper range value).Gl(sg liquid at 15 oC).sq(square).Gf(sg liquid at process). . (time or x)
Gas flow is Qe = (0.593).(Q).sq of T.G/P
0.593(constanta).T(temp abs gas in oK).G(sg process gas).P(Pressure abs gas in kPa).
10/03/2010 9:30 AM
No Dear
i want calibrate a differential flow transmitter,its range is 0 to 500 mbar
at the time of calibration in 0 the output should be 4 mA & at 500 mabr the output should be 20 mA,in liniarly i get 125 mbar -8 mA,250 -12 mA,375 mbar-16 mA
BUT the transmitter flow range is in squre root , at the time of calibration in
0 mbar - i got 4 mA and 500 mbar-20 mA,but other outputs are different, CAN any one solve my problems
10/20/2010 3:41 PM
at 25% of 500mbar ie 125mbar you will get 12mamp.at 50% ie 250mbar you will get 15.31 mamp.at 75%ie 375mbar yuo will get 17.856mamp 500mbar 20mamp
10/14/2010 7:32 AM
can you try squaring the signal with a multiplier ic and using the output
10/15/2010 8:37 AM
Guest,
This is the second time you've inquired on this forum about the same issue.
Please explain what you are attempting to accomplish by answering each of the questions below.
What do you mean by 'calibrate'?
Is the transmitter functioning as it should in the process and you are just checking its output against a pressure source?
It is apparent that the transmitter is set up for square root output. Is it supposed to be a square root output?
What is it that you expect to be able to do with the equipment at hand?
Since you can read the current output at various pressure levels, what roadblock are you encountering?
What brand and model pressure transmitter are you working with?
What brand and model calibrator?
You might be interested in: Flow Meters, Utility Meters, Air Velocity Flow Sensors