Please get more educated on pf correction. Capacitors are used for this of course. Switching of these capacitors as needed is best done by special contactors meant for this duty, spcifically called AC6b as per IEC 60947-4. They are used because (a) they can attenuate the very high inrush currents of parallely switched capacitors and (b) they have a very long life, in millions of operations, as opposed to any CBs which are not likely to last more than a few thousands of operations mechanically.
Please download and read this document as a start : abb
__________________
Nothing worthwhile can ever be taught, it can only be learnt.
you're talking about pf correction..yet what you employ were MCCB's..check-out your power triangle/impeadance triangle..and see what affects your power factor...