Alternator Parellel Operation

10/07/2010 7:56 AM

if three alternaters are running in parrelel and connected to 50 hz infinite bus,if one of the alternater frequency increses wt will hapens?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: Alternator Parellel Operation

10/07/2010 9:27 AM

Simple! It will try to "swallow" more kW load from the infinite bus. In the process its speed will "droop" and its frequency will fall. This will happn until the alternator frquency is equal to the bus frequency.

Register to Reply
Anonymous Poster
#2
In reply to #1

Re: Alternator Parellel Operation

10/07/2010 9:59 AM

It will try to "swallow" more kW load from the infinite bus

Infinite bus will try to "swallow" more kW load from it...

Register to Reply Off Topic (Score 5)
Participant

Join Date: Oct 2010
Posts: 3
#4
In reply to #1

Re: Alternator Parellel Operation

10/12/2010 7:15 AM

in which form the excessive energy consumes? u saying bus will swallows the energy,but in which form,and what abt load sharing?and frequency of the other alternators?

Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#3

Re: Alternator Parellel Operation

10/07/2010 7:14 PM

The generators frequency (or the speed) is controlled by the prime mover's governor which controls the input power (generally fuel) of the prime mover. The governor has two types of control mode: Isochronous mode and Droop mode with a droop setting. With isochronous mode, the governor always keeps the frequency constant with increasing or decreasing the fuel (and thus shares the load), while the droop mode shares the load based on the system frequency. See the thread http://cr4.globalspec.com/thread/42805/Electrical-Governor-Settings for more detail.

If your generators run in parallel with the utility supply, they are generally set in droop mode. When you said, one of the alternator frequency increases, I assumed you do it by manually applying the increase signal to its governor. In this case, the generator will deliver more power to the system and if the load remains constant, the same amount of power will be decreased from the utility supply. Other two generators load will remain constant. However, the load sharing philosophy will be different if the governor of one of the other two generators is set in isochronous mode.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Power-User
Hobbies - HAM Radio - New Member

Join Date: Oct 2008
Location: Houston, Texas
Posts: 252
Good Answers: 5
#5

Re: Alternator Parallel Operation

01/11/2012 3:06 PM

If the connected bus is truly infinite and actually running at 50Hz, nothing any of the three alternators does can affect the frequency. Typically the machines are running in droop and if this is the case, the machine with the higher setpoint will pickup proportianately more load than the machines with lower setpoints.

Have FUN!

TT3

__________________
If the software can detect, compensate, avoid, or correct an anomalous condition in the system, it is, by definition, a software problem-regardless of the root cause. In the long run, for most classes of problems, it is cheaper to fix it in the SW
Register to Reply
Register to Reply 5 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); electricalexpert65 (1); Eshwar92 (1); msamad (1); Turbotroll3 (1)