The AREVA MiCOM Feeder Management Relay (P14x series) has both 1A and 5A current ratings and they have the separate terminals for the connection. See the 'Technical Data Sheet' for MiCOM P141/2/3 (Feeder Management Relays) for detail.
In Page 8, see "AC Current: Nominal current (In): 1A and 5A dual rated. (1A and 5A inputs use different transformer tap connections, check correct terminals are wired)".
For the wiring diagram, see the pages 32 through 44 for the connection details of 1A and 5A terminals. The 1A input is connected to the terminals C2, C5, C8, C11 and C14, while the 5A input is connected to C1, C4, C7, C10 and C13.
So, you can use either 1A CT or 5A CT with wiring them to the correct terminals.