Hitachi Chiller Problem

10/10/2010 12:17 AM

Does anybody having experience of Hitachi Chiller ,Model RCUP46AUZ (refrigerent 407C);we have the insufficient cooling ie. chilled water inlet temperature and outlet temperature is same 10 degree C.

We have done all possible actions but no remedies,even we clean the Heat exchanger also but no good result.

Register to Reply
Pathfinder Tags: chiller problem
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Hitachi chiller problem

10/10/2010 12:32 AM

Do you have any information on the suction and discharge pressures of the compressor, or the appearance of liquid/bubbles/vapor in the sight glass? Is the unit actually running?

One guess might be that there is a leak in the system, with loss of refrigerant charge.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Commentator

Join Date: Oct 2010
Posts: 55
Good Answers: 2
#2

Re: Hitachi Chiller Problem

10/10/2010 9:49 PM

Insufficient cooling? The inlet and outlet temperatures are the same indicating no cooling is being done. This unit rated at 5-15 degree C. outlet temperature. Without a complete list of the operating conditions there is no good solution to be offered for your problem. The inlet temperature would indicate that there is no load for the unit to cool. Without a higher inlet temperature the unit controls may well not even be calling for the compressor to start. I would start by checking the sequence of operation for this unit for the application it is being used on.

Register to Reply
Guru

Join Date: Jun 2008
Location: Oman
Posts: 612
Good Answers: 14
#3

Re: Hitachi Chiller Problem

10/11/2010 12:03 AM

Some of the causes are:

No cooling load on the system

Shortage of refrigerant

Defective compressor valves

Air or condensate in system

Wrong expansion valve super heat setting

Dirty or defective expansion valve

Restriction in refrigerant circuit.

Dry coils.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member India - Member - New Member

Join Date: Aug 2008
Location: City of destiny, INDIA
Posts: 775
Good Answers: 67
#4

Re: Hitachi Chiller Problem

10/11/2010 8:19 AM

How much should be chilled water inlet temperature and outlet temperature?

Please check suction and discharge pressure of compressor. If compressor is running you will find difference in it. If these pressures are normal, evaporator must be evaporating some liquid refrigerant and giving cooling effect. From your incomplete narration of problem I suspect either of the following:

1. You do not have cooling load & compressor is automatically switched off. Suction and discharge pressure of compressor shall be same in this case. Compressor kW or Amps will be Zero.

2. Motor & compressor got disconnected and only motor is moving. Suction and discharge pressure of compressor shall be same in this case also. Compressor kW or Amps will be Zero.

3. Your system lost refrigerant considerably due to leak somewhere. Check operating parameters and evaporator liquid level to confirm.

4. Lube oil got mixed-up with refrigerant in abnormal proportion (some mixing-up may be allowed). Higher lube oil consumtion in previous weeks can be checked. Being lighter compared to refrigerant oil will float on top of refrigerant level in evaporator and reduce evaporation which is required for cooling. This in combination of sl. no. 3 above is desasterous.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member India - Member - New Member

Join Date: Aug 2008
Location: City of destiny, INDIA
Posts: 775
Good Answers: 67
#5
In reply to #4

Re: Hitachi Chiller Problem

10/11/2010 8:29 AM

I want to correct sl no. 2 of my preceding post.

Instead of "Compressor kW or Amps will be Zero" please read

"Compressor kW or Amps will be abnormally low- required for motor no load run."

Register to Reply
Anonymous Poster
#6

Re: Hitachi Chiller Problem

10/12/2010 7:17 PM

If the water flow through the cooler barrel is 2, 3, or 4 pass, consider the possibility that water is slipping pass a separator plate in an end bell and bypassing the heat exchanger

Register to Reply