Grounding a 3 Phase 480V Transformer

10/10/2010 3:17 AM

I need some assistance with grounding on a 3 phase 480v transformer that is feeding a MCC. The issue is that I have measured as much as 30 amps in the ground cable and have experienced numerous ground faults. My suspicion is that this is creating circulating currents in the throttle signals out to my generator sets as I am getting distortion on my PWM signals at low load sufficient to shut the generator down on a PWM fault. This is on a land oil drilling rig.

Can someone explain what the correct transformer connection configuration should be for the neutral on a 3 phase WYE feeding an MCC in this environment? What is here looks to be a grounded neutral, I am reading 277 to ground on all three phases but nothing trips when it shorts to ground. My biggest concern beyond the control issue is the potential for an arc with the current in the ground cable.

Thanks for the assistance.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Participant

Join Date: Oct 2010
Posts: 3
#1

Re: Sleuth

10/10/2010 4:15 AM

You're suspicion has high probability of being correct. What is the connection of your transformer and how is it grounded?

http://transmissiondesignhub.blogspot.com

Register to Reply
Participant

Join Date: Oct 2010
Posts: 4
#7
In reply to #1

Re: Sleuth

10/15/2010 11:23 PM

Thank you for you input, I am in a remote spot in Asia and my email is not what I would like it to be sorry for the delay in responding.

The transform is Delta Delta, and the only ground is at the frame there is no neutral.

Register to Reply
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#2

Re: Sleuth

10/10/2010 3:40 PM

Grounding conductor is to be connected at the star point of the transformer winding, Neutral cable termination is also precisely at the same spot.

If you measure at No-load there will be insignificant current flow in neutral.

Start switching On the load circuit breakers one by one and keep checking the flow of current in Neutral. Pin point the defective feeders causing flow in neutral.

I guess single phase loads such as lights are not equally distributed on phases.

__________________
Knowledge sharing is a WIN-WIN situation
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#3

Re: Sleuth

10/10/2010 6:13 PM

Please describe the primary side of this transformer and what if any interconnections exist between the two separetly derived systems. This almost sounds like the neutral at the MCC is tied to ground, which it should not be. What is it that should trip that is not?

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Member

Join Date: Sep 2010
Posts: 8
#4
In reply to #3

Re: Sleuth

10/10/2010 11:46 PM

To clarify:

The system should have only one point where the Neutral is connected to Ground. Any other inadvertent tie points will result in Ground Loops.

Register to Reply
Participant

Join Date: Oct 2010
Posts: 4
#8
In reply to #3

Re: Sleuth

10/15/2010 11:41 PM

The transformer is a Delta, Delta, there is no neutral, the ground is tied to the frame of the transformer. Having said that I have found multiple ground loops. The MCC feeds a lighting transformer, that then in turn has the neutral and ground bonded at the panel. I suspect that there are swapped neutrals and grounds in the field wiring.

Thanks for the help.

Register to Reply
Associate

Join Date: Jun 2010
Location: INDIA
Posts: 27
Good Answers: 1
#5

Re: Grounding a 3 Phase 480V Transformer

10/11/2010 12:50 AM

Check the Transformer 480Volt connection side if neutral is solidly grounded or not.

If neutral configuration demands solidly grounded then the neutral grounding is improper.

For oil rigs I think neutral is impedance grounded .

There are systems in 480volt whetre neutral is not solidly grounded this case NGR/NGT is applied.

In such cases you will get only 3phase loading,for single phase loading is not possible with this system.

There must be some spurious single phase loading existing and this is causing current in the ground cable .

For single phase loading you should have 480/277 transformer neutral ungrounded.

For Three phase overcurrent protection the connection is same as three phase overcurrent residually connection the only thing the 50/51N earthfault relay is not applied in the residual path.

For earth Fault you should have a CBCT and very sensitive earthfault relay

The CT neutral has to be grounded at one end nearest to the relay.

HOPE THIS SETTLES YOUR QUERRY.

__________________
S BHATTACHARYA
Register to Reply
Power-User
Engineering Fields - Control Engineering - Control Engineering Technical Fields - Education - Industrial Training Engineering Fields - Manufacturing Engineering - Manufacturing Training Engineering Fields - Electrical Engineering - Electrical engineering Training Engineering Fields - Instrumentation Engineering - Instrumentation Engineering United States - Member - New Member Engineering Fields - Energy Engineering - Become part of the larger group, change your world.

Join Date: Apr 2005
Location: Las Vegas, NV
Posts: 266
Good Answers: 1
#6

Re: Grounding a 3 Phase 480V Transformer

10/14/2010 8:24 AM

For your reference, you may find Larry Bush's ebook with practicle knowledge on generators of help.

Also the Industrial Electrical course, sample video below...

http://www.youtube.com/v/QNdMrPQMb1E

__________________
AB PLC Training onsite, On-Line, training software and more. BIN95.com
Register to Reply
Participant

Join Date: Oct 2010
Posts: 4
#9

Re: Grounding a 3 Phase 480V Transformer

10/16/2010 12:00 AM

I was incorrect in stating that the transformer was WYE configured on the secondary, it is actually a Delta, Delta, transformer and there is no neutral connection. The ground is only on the frame of the transformer. Having said that I get roughly 270vac to ground. I am not sure what I should be seeing to ground any assistance here would be appreciated.

There are multiple ground loops and as much as 35 amps on one jumper between the ground bus between MCC'S, there are 2. My suspicion is that possibly neutrals and grounds have been swapped in the field from the lighting panel. I guess that it might be possible to induce the current in the cable if it were placed in a wire way beside 480vac motor power if the run were long enough.

I am also able to see as much as 300 HZ when checking the frequency without using a low pass filter.

Thanks again

Register to Reply