Anonymous Poster

Motor Issue

10/10/2010 5:14 AM

Hi

I have a 60hp motor operated with a star delta starter when the starter is moving from star to delta the motor is getting stalled with spark in star contactor, and the starter is in on state but the motor is stalled

please could you help me to solve this problem

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Motor Issue

10/10/2010 5:44 AM

Does the delta contactor close?
Or does the supply trip?

__________________
The reports of my death are greatly exaggerated.
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#2

Re: Motor Issue

10/10/2010 7:05 AM

As the motor is able to start in Star, there is no possibility that it is stalling due to mechanical overload in delta (the torque in delta is 3 times that in star).

You say there is a spark in the Υ contactor, but is it very severe? It may have welded, thereby preventing changeover to delta ?

Is there short-circuiting of the incoming supply when it changes from Υ to Δ ? This is quite common if there is no 'transition delay' of at least 30 ms between Υ contactor dropping and Δ switching on.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#3

Re: Motor Issue

10/10/2010 12:30 PM

sounds like you have your connections the wrong way around, check those first then the SD starter checking the contacts, also the time taken for the change over, is it manual or automatic?

__________________
The square root of nothing is what you make it!
Reply