Power Cable Size

10/12/2010 12:56 AM

Hi ,

We have PLC( Programmable Logic Controller ) Based Panel ,With load of 10 A including all Spare slot/Input-Output Modules

Panel has one Main Circuit Breaker of 32 A and then will be Connected to UPS (Uniterruptible Power supply ) by Power Cable PC-001

Question is, If we have to size for Power Cable PC-001, We should consider 10A or 32 A as Load

Regards

Jose

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: Power Cable Size

10/12/2010 3:27 AM

The cable protected by (i.e. downstream of) the 32A breaker (which I think is what you're asking about, if I read you correctly) should be sized for 32A.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Score 1 for Good Answer
Participant

Join Date: May 2008
Location: Hyderabad-INDIA
Posts: 4
#2

Re: Power Cable Size

10/12/2010 3:04 PM

The cable should be considered to bear the load of 32 A as the Main Circuit Breaker is of 32 A.

If you consider the cable of 10 A and in case of load increases higher that 10 A, then your cable will first get affected before Main Circuit Breaker trips the circuit.

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#3

Re: Power Cable Size

10/12/2010 5:31 PM

Please explain your question more clearly.

So far you have one answer which will keep you safe (but may be more expensive than necessary), and one which may not stop your cable and surroundings bursting into flames (in the event of a fault) - depending on your wiring.

The appropriate cable rating depends critically on your layout.

Also, please explain "Power Cable PC-001". Is this an assembly supplied by a manufacturer? If so, please give the details.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Power-User

Join Date: Mar 2008
Location: Mumbai
Posts: 250
Good Answers: 2
#5
In reply to #3

Re: Power Cable Size

10/13/2010 2:47 AM

http://ifile.it/7k2jr8l/PS%201.bmp

http://ifile.it/xjszt5b/power%20consump.bmp

The distance between PLC &UPS is 20 M, Will be routed Through Riased Floor.This is not a complex layout --Straight Run

PC-001 ( 02 Core Cable )is to be Procured by us, It will be connected between PLC (32A MCB) & UPS system

Gents , Thanks For all Your Info.

Regards

Jose

Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#7
In reply to #5

Re: Power Cable Size

10/13/2010 5:05 AM

All cable upstream of the 6A fuses must be rated at 32A or greater.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Associate

Join Date: Oct 2010
Posts: 42
Good Answers: 5
#4

Re: Power Cable Size

10/13/2010 12:50 AM

I think you will find that the cost difference between a power cable able to provide 10A and one that will provide 32A is negligible for the length between the UPS and the panel.

If the length between these two is so great as to cause concern in price difference, then you have a larger issue to concern yourself with, wire resistance.

In any case, it is better to provide the breaker with the proper supply line even if the UPS is only a 1200W UPS. You never know what future technicians may do and you do not want your supply cable to be the weak link.

So there are 3 solid reasons to supply the panel with a 32A Power Cable.

1. Negligible Cost Differential

2. Lower wire resistance

3. Compatible power path.

Alternatively, you may wish to lower the 32A rating to 15A throughout:

1800W UPS

15A Power Cable

15A Circuit Breaker

This configuration relaxes some of the electrical requirements, keeps the power system compatible and still affords a 5A (50%) overhead above the load values.

Register to Reply
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#6

Re: Power Cable Size

10/13/2010 4:24 AM

Why don't you replace the 32 amp MCB with a 10 amp MCB. I also find it hard to belive that the PLC requires a supply of 10 amps.

Cheers

Joe

Register to Reply
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#8

Re: Power Cable Size

10/13/2010 6:18 AM

I suppose I should ask this question, how many outputs are there on this PLC?

The reason that I ask this is that the PLC outputs are probally rated at 3 amps at 230vac each. Are you, or has someone else summed up the total output current and decided on the 32 amp MCB?

I would in my design never over-rate a PLC outputs if the current of each output is only 3 amps, there is no way that I would be using a 32 amp MCB, if you have a fault you will blow the output module up before the MCB would tripp!

When ever i use a plc i design the system so that it would protect the output circuits of the plc, but having a 10 amp mcb or greater and if you have a fault, be prepaired to have replace the plc.

It is most inportant that when deciding the MCB size that it is rated for the maximum current of one of the outputs, not the sum of the outputs.

I have never seen a Plc that has an output ratting of 10 amp's let alone 32 amp's. take a serious look at the loading of the plc and get things right.

32 amp mcb connected to a plc gives me shivvers, there is no way i would go there, even 10 amps would worry me.

Cheers

Joe

Register to Reply
Associate

Join Date: Oct 2010
Posts: 42
Good Answers: 5
#9
In reply to #8

Re: Power Cable Size

10/13/2010 8:02 PM

I think he said it was a PLC panel.

Imagine if that panel was equipped with these: http://www.seltec.co.uk/products/details/8771.html

Then the Panel CB would need to protect it while still affording the full range of capability.

Register to Reply
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#10
In reply to #9

Re: Power Cable Size

10/13/2010 9:25 PM

I thought he said with a load of 10 Amp.

Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#11
In reply to #10

Re: Power Cable Size

10/14/2010 2:34 AM

Did you check out his links in #5?

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Power-User
South Africa - Member -

Join Date: Nov 2008
Location: Johannesburg
Posts: 295
Good Answers: 12
#12

Re: Power Cable Size

10/14/2010 7:01 AM

Hi there,

Please download the following handbook. It will give you some insight on how to size your power cables correctly.

You can download the whole handbook or just pieces of it - but rather get the whole handbook.

Off the top of my head.

You have a 10A load at 20m distance and this cable would probably not be buried.

You have a 32A breaker. The breaker is here to protect the cable if you're not using fuses. You are only allowed a certain percentage volt drop - country specific. If you are not using fuses - your cable would have to have a bigger current carrying capacity than your breaker rating - otherwise the cable will become the fuse in the case of a fault.

If you are using the circuit breaker to protect the cable - the smallest cable size you could use would be 6mm which can carry 40A without being de-rated. This would be overkill as you could have probably used a 2.5mm cable and protected it with a 15A breaker.

Either way - have a look at the book and it will give you some insight as to how we size power cables.

Regards,

Craig

Register to Reply
Active Contributor

Join Date: Nov 2010
Location: INDIA
Posts: 19
#13

Re: Power Cable Size

11/08/2010 4:45 AM

obviously 32 amp.......

__________________
SHAIKH QAMAR AZAM // INSTRUMENT ENGINEER
Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#14
In reply to #13

Re: Power Cable Size

11/08/2010 6:16 PM

"obviously 32 amp......." is not helpful to the OP or anyone else in the discussion unless you explain why. "Why" has already been explained. Your post is redundant.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Register to Reply 14 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

craigza (1); hamid918 (1); Joe Sparky (3); JohnDG (5); josej (1); q_qamar4u (1); URAD_Harvey (2)