Comparison of Generator with Same Insulation Class & Different Class Temp. Rise

10/17/2010 3:59 AM

If asked to make a selection among two generators 25 MW each with one having Insulation class F and Temp rise F and other insulation class F with Temp rise limited to class B. The selection is very obvious, the Machine with insulation F with Temp rise limited to class B.

Will you pl. share your experience when comparing two machine with respect to Iron loss, Copper loss, total power loss in machine, flux density at normal operation, expected life, reliability, and over load capabilities, cost etc

any web links on subjects Pl.

__________________
When was last time you did something for first time.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: Camparision of Generator with same issulation class & different class temp. rise

10/17/2010 4:29 AM

You have asked this before as a guest? Despite 30 views, no answers. Maybe i should not be giving my views here since i am no expert in generators, but....

... if you are using Class F insulation, why would you restrict yourself to Class B temperature rise? Overkill isn't it? 50°C is the margin. Why so much overdesign?

i can understand this if this was a fire-pump or something similar, where the risk of loss of life is there...not in a generator.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#2
In reply to #1

Re: Camparision of Generator with same issulation class & different class temp. rise

10/17/2010 5:34 AM

As generator is important piece of equipment, so selecting Insulation class F and temp rise limited to class B shall result in extending service life of generator.

As there is thumb rule any increse/fall of 10 dig operating temperature half/double the useful life of insulation of 20,000 hrs.

Any further readings on subject, pl suggest.

__________________
When was last time you did something for first time.
Register to Reply
Power-User

Join Date: Mar 2010
Location: BHOPAL, INDIA
Posts: 201
Good Answers: 20
#3

Re: Comparison of Generator with Same Insulation Class & Different Class Temp. Rise

10/21/2010 12:18 AM

You have posted the question in last 3-4 days and I had posted my reply today. please see the same

Register to Reply Score 1 for Good Answer
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#4
In reply to #3

Re: Comparison of Generator with Same Insulation Class & Different Class Temp. Rise

10/21/2010 6:21 AM

Dear PCCHATUR,

Thanks for reply.

Will you pl. suggest values of flux density (or corel loss in Watts/KG of iron core) for two machines of 25 MW with Insulation class F and different temp class rise.

I hope you to have answer...

__________________
When was last time you did something for first time.
Register to Reply
Power-User

Join Date: Mar 2010
Location: BHOPAL, INDIA
Posts: 201
Good Answers: 20
#5
In reply to #4

Re: Comparison of Generator with Same Insulation Class & Different Class Temp. Rise

10/21/2010 11:25 AM

Generators are not designs are not changed for such features (Class F temperature rise and class B temperature rise). Each generator is designed for a particular MVA rating using class insulation with class B temperature rise. If you ask for generator with class F rise, you will be offered a smaller MVA generator to be operated at your asked rating which will have class rise at this rating.

As far flux density or watts/Kg for two generators, steel grade is not changed for such changes. Generally 1.5W/Kg grade of steel is used for Turbo Generator core design.

Register to Reply Score 1 for Good Answer
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#6
In reply to #5

Re: Comparison of Generator with Same Insulation Class & Different Class Temp. Rise

10/22/2010 2:50 AM

I assume the figure loss in iron 1.5W/Kg is for Machine with insulation class F and temp rise class B.

What would be figure of iron loss for Machine with insulation class F and temp rise class F. I mean iron loss value at operating point.

Again I hope you have answer.

Thanks in advance for your answer.

__________________
When was last time you did something for first time.
Register to Reply