In relay testing, pre-fault is the length of time you program your test set to output normal ("pre-fault") conditions of voltage & current. Pre-fault voltage would usually be nominal voltage conditions for that state. Most relays need to sense nominal system conditions for some pre-set time to know the system is stable before you can apply fault conditions and expect it to act properly on them.
Max fault time is the length of time the simulated fault conditions are applied to the relay under test by the test set. It would be a set of voltage and current values at appropriate phase angles that represent a phase-ground or phase-phase fault at some specific distance from the terminal, for which you have calculated expected values, and the relay is expected to pick up and trip in a predetermined time.
Post-fault time the length of time you program the test set to give expected post-fault conditions of voltage & current tothe relay, i.e., what it is expecting to sense once it has tripped the circuit breaker or whatever the action it is supposed to initiate.
__________________
To get the right answers, first you need to ask the right questions.
is this means the test set will output nominal relay volts and amperes for 1.5sec then fault volts and amperes for 3.0 sec ? i realy dont get the idea of post fault voltage and current.
It could be used for example in reclosing schemes, where the measured quantities return to some nominal value after tripping a circuit breaker, and then apply the fault again when the breaker is reclosed. It could also be used for breaker failure schemes where a pole (or multiple poles) of a breaker doesn't trip and you want to simulate what conditions are so that backup relays will function. Anything where you need to apply different conditions after the trip signal is given by the relay.
__________________
To get the right answers, first you need to ask the right questions.