Overvoltage Limit Alarm on Sag Mill

10/17/2010 7:41 PM

we have two big loads at our mine, the sag and the ball mill with 18MW and 16MW respectively. now adays we are experiencing a trip out on the sag mill on stator overvoltage limit alarm but the ball mill continues to ran with no problems. what could be the reason? the ball mill is usually loaded to about 90% full load capacity. please help.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor

Join Date: Sep 2009
Posts: 13
#1

Re: overvoltage limit alarm on sag mill

10/17/2010 7:44 PM

just to add on the above, the sag is usually loaded to about 70% load capacity.and runs at 7 RPM and the ball mill runs at 11 RPM.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Overvoltage Limit Alarm on Sag Mill

10/18/2010 4:56 AM

Is the alarm coming up on start up?

I'm thinking back to a problem I had with a mill where it would stall after about ¼ of a turn and then run back slightly until the torque was high enough to continue. We sort of cured the problem by leaving a higher burden in the mill on shut down.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Overvoltage Limit Alarm on Sag Mill

10/18/2010 12:58 PM

Is it a synchronous motor? If so, are you perhaps slipping a pole? If so, OV trips could be the least of your problems.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#4

Re: Overvoltage Limit Alarm on Sag Mill

10/18/2010 2:26 PM

Have you monitored the line voltage during the event?

__________________
CRTL-Z
Register to Reply
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#5

Re: Overvoltage Limit Alarm on Sag Mill

10/18/2010 11:56 PM

We also faced similar problems;

Detailed investigation in one case revealed that someone has changed transformer tap position during preventive maintenance and in another case the protection relay was contaminated with dust and moisture causing malfunction.

__________________
Knowledge sharing is a WIN-WIN situation
Register to Reply
Active Contributor

Join Date: Sep 2009
Posts: 13
#6
In reply to #5

Re: Overvoltage Limit Alarm on Sag Mill

12/09/2010 12:37 PM

we kind of switched the excitation control cards from the ball mill to the sag and vice versa and it seems we have sorted out the problem though not very convinced. the problem has since stopped. no loose connections were found in the process so i still do not understand the problem. any way atleast it'e working for now. thanks for all you contributions